[Bldg-sim] Per 90.1, mass wall or steel-framed wall?

Chris Baker ChrisB at TWGI.com
Fri May 3 07:49:00 PDT 2013


Ramana,

 

Per Table G3.1 section 5b, the baseline is always a steel-framed wall
for Appendix G modeling. So you get to take credit for additional
thermal mass.

 

Chris Baker 

AIA, PE, BEMP, BEAP,
LEED AP BD+C

THE WEIDT GROUP(r)
 

5800 Baker Road
Minnetonka, MN 55345
T 952.938.1588
F 952.938.1480
twgi.com <http://twgi.com/> 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Friday, May 03, 2013 9:37 AM
To: Bldg-Sim
Subject: [Bldg-sim] Per 90.1, mass wall or steel-framed wall?

 

Dear all,

 

For a LEED EAp2/EAc1 energy model, does the following above-grade wall
situation fall under a mass wall or a steel-framed wall in the baseline?

 

8" CMU wall (load bearing) with steel studs to the interior just to
create a cavity for the batt insulation etc.

 

Thanks,

Ramana Koti.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/1aad2e43/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1199 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/1aad2e43/attachment-0002.gif>


More information about the Bldg-sim mailing list