[Bldg-sim] Baseline VAV OA vs Proposed DOAS OA
韩星
foolishstar at 163.com
Fri May 10 07:43:27 PDT 2013
In my opinion, the baseline case OA should be equal to the proposed OA. OA required by 62.1 is only a basis for reference.
Xing
At 2013-05-10 22:32:56,"Dónal O'Connor" <oconnor_dj at hotmail.com> wrote:
Hi all,
I'm looking for guidance on which number to use for my baseline OA when compared to the proposed system.
The proposed HVAC system is DOAS - FCUs. OA requirements according to ASHRAE 62.1 are 10,216 cfm. However, to satisfy exhaust requirements, the total system ventilation, i.e. OA as it's a DOAS, is 13,160 cfm.
Does the baseline OA need to equal 10,216 or 13,160 cfm?
Thanks
Dónal