[Bldg-sim] Modelling Infiltration for Low Energy Houses

Francesco Passerini fpasserini.tn at gmail.com
Tue May 28 03:14:45 PDT 2013


I have read that also the object
AirflowNetwork:MultiZone:Component:DetailedOpening
can be used to model infiltration. See here:
http://tech.groups.yahoo.com/group/EnergyPlus_Support/message/28251
With Regards
Francesco Passerini


---------- Forwarded message ----------
From: <bldg-sim-request at lists.onebuilding.org>
Date: 2013/5/27
Subject: Bldg-sim Digest, Vol 66, Issue 22
To: bldg-sim at lists.onebuilding.org


Send Bldg-sim mailing list submissions to
        bldg-sim at lists.onebuilding.org

To subscribe or unsubscribe via the World Wide Web, visit
        http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
or, via email, send a message with subject or body 'help' to
        bldg-sim-request at lists.onebuilding.org

You can reach the person managing the list at
        bldg-sim-owner at lists.onebuilding.org

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Bldg-sim digest..."

Today's Topics:

   1. Modelling Infiltration for Low Energy Houses (Hayes Zirnhelt)
   2. Re: Modelling Infiltration for Low Energy Houses (Shaun Martin)


---------- Messaggio inoltrato ----------
From: Hayes Zirnhelt <hzirnhelt at hotmail.com>
To: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Cc:
Date: Mon, 27 May 2013 09:40:13 -0700
Subject: [Bldg-sim] Modelling Infiltration for Low Energy Houses
Hi,

I've created a detailed multi-zone model of a low energy home in Canada in
EnergyPlus. I am looking at the peak heating load results and finding that
the infiltration predicted seems quite high. I'd be interested to hear how
other building modellers are approaching infiltration, and any general
thoughts anyone has on this situation.

The model is based on the design - the house has not been constructed yet,
but it is assumed that an ACH at 50pa rating of 1 can be achieved. EnergyPlus
has a simple infiltration modelling option, where the air leakage can be
input as ACH@ regular pressure (I've assumed this is equal to 1/20 = 0.05).

EnergyPlus's basic infiltration model can adjust the infiltration rate for
delta T and windspeed, using the following formula:

Infiltration = I_design * {A + B (T_zone - T_outdoor) + C*windspeed +
D*windspeed^2 }****

** **

The big question I have is what coefficients should be used? EPlus provides
three suggestions:


1. coefficients from BLAST:


A =     0.606,                   !- Constant Term Coefficient****

B =     0.03636,                 !- Temperature Term Coefficient****

C =    0.1177,                  !- Velocity Term Coefficient****

D =    0;                       !- Velocity Squared Term Coefficient


2. coeffs from DOE: 0, 0, 0.224 (windpeed), 0


3.Default: 1,0,0,0 which means a constant ACH with no modification.


The BLAST coefficients seemed to be the best to me because I think wind and
temperature difference should be accounted for and there should always be
some basic infiltration. However, using these coefficients at the peak
heating load condition (delta T ~ 40C, windpeed = 27 km/hr) the
infiltration rate is tripled from the base 0.05 ACH, and the total load
from infiltration equals 2.2 kW, which is the largest component of the
heating load.


For a relatively tight house this seems like an unrealistic value to me,
but I do not have much to compare it against.



Thanks,


Hayes


Hayes Zirnhelt, M.A.Sc****

EcoOptimal Building Energy Analysis****

hayes at eco-optimal.ca****

www.eco-optimal.ca****

T: 778.961.0086



---------- Messaggio inoltrato ----------
From: "Shaun Martin" <smartin at shaunmartinconsulting.com>
To: "'Hayes Zirnhelt'" <hzirnhelt at hotmail.com>, <
bldg-sim at lists.onebuilding.org>
Cc:
Date: Mon, 27 May 2013 11:39:03 -0700
Subject: Re: [Bldg-sim] Modelling Infiltration for Low Energy Houses

Hi Hayes,****

** **

The ZoneInfiltration:EffectiveLeakageArea approach in E+ might give you
better results as it is tailored for residential buildings.  It accounts
for stack, wind and sheltering better than the
ZoneInfiltration:DesignFlowRate method, which is used more for larger
building models.  ****

** **

Regardless of the method, the bigger problem is the infiltration schedule.
You could start with the schedules they have in eQuest.   The operation of
the HRV will affect the infiltration schedule.  And, on larger buildings,
of course, infiltration in core zones can be set to zero.****

** **

On a 600m3 house, ACH50 = 1.0 is roughly 166 L/s.  This is about 55 L/s at
10Pa,  and translates to an effective leakage area of about 0.45 cm/m2.
These are what I would use as design numbers.   From experience, ACH50 =
1.0 (even 1.5) is a challenging target to reach and can’t be reached unless
you use a blower door during construction.  ****

** **

Hope this helps,****

Shaun****

****

** **

*From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Hayes Zirnhelt
*Sent:* Monday, May 27, 2013 9:40 AM
*To:* bldg-sim at lists.onebuilding.org
*Subject:* [Bldg-sim] Modelling Infiltration for Low Energy Houses****

** **

Hi,****

** **

I've created a detailed multi-zone model of a low energy home in Canada in
EnergyPlus. I am looking at the peak heating load results and finding that
the infiltration predicted seems quite high. I'd be interested to hear how
other building modellers are approaching infiltration, and any general
thoughts anyone has on this situation.****

** **

The model is based on the design - the house has not been constructed yet,
but it is assumed that an ACH at 50pa rating of 1 can be achieved. EnergyPlus
has a simple infiltration modelling option, where the air leakage can be
input as ACH@ regular pressure (I've assumed this is equal to 1/20 = 0.05).*
***

** **

EnergyPlus's basic infiltration model can adjust the infiltration rate for
delta T and windspeed, using the following formula:****

** **

Infiltration = I_design * {A + B (T_zone - T_outdoor) + C*windspeed +
D*windspeed^2 }****

 ****

The big question I have is what coefficients should be used? EPlus provides
three suggestions: ****

** **

1. coefficients from BLAST:****

** **

A =     0.606,                   !- Constant Term Coefficient****

B =     0.03636,                 !- Temperature Term Coefficient****

C =    0.1177,                  !- Velocity Term Coefficient****

D =    0;                       !- Velocity Squared Term Coefficient****

** **

2. coeffs from DOE: 0, 0, 0.224 (windpeed), 0****

** **

3.Default: 1,0,0,0 which means a constant ACH with no modification.****

** **

The BLAST coefficients seemed to be the best to me because I think wind and
temperature difference should be accounted for and there should always be
some basic infiltration. However, using these coefficients at the peak
heating load condition (delta T ~ 40C, windpeed = 27 km/hr) the
infiltration rate is tripled from the base 0.05 ACH, and the total load
from infiltration equals 2.2 kW, which is the largest component of the
heating load.****

** **

For a relatively tight house this seems like an unrealistic value to me,
but I do not have much to compare it against.****

** **

** **

Thanks,****

** **

Hayes****

** **

Hayes Zirnhelt, M.A.Sc****

EcoOptimal Building Energy Analysis****

hayes at eco-optimal.ca****

www.eco-optimal.ca****

T: 778.961.0086****

_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130528/b12aee2e/attachment-0002.htm>


More information about the Bldg-sim mailing list