[Bldg-sim] Baseline system type for fossil fuel/electric hybrid
Duggin, Cory
Cory.Duggin at tlc-eng.com
Thu Jan 16 08:02:47 PST 2014
The predominant condition is the one that serves the largest conditioned area. This note is referring back to G3.1.1 exception a which allows the use of additional baseline system type(s) for non-predominant conditions if they are greater than 20k ft2.
Cory Duggin, EI
Energy Engineer I
direct: 615-346-1939
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nicholas Blanton
Sent: Thursday, January 16, 2014 9:55 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Baseline system type for fossil fuel/electric hybrid
Hello,
A project I'm building the energy model for is considering switching to electric heat. I understand that generally you would use the predominant HVAC system, so if the "predominant" system is electric, you would use System 8. See highlighted excerpt below.
My question to you is: what qualifies as "predominant"? Is there some percentage of energy consumption assigned to gas and electricity that signifies either as being dominant?
Thank you for the clarification.
[cid:image001.jpg at 01CF12A2.1BB62EC0]
Nicholas E Blanton
Mechanical Engineer | Graduate
Arup
1120 Connecticut Avenue NW Suite 1110 Washington DC 20036 USA
t +1 202 729 8220 d +1 202 729 8241
m +1 505 228 4154
www.arup.com<http://www.arup.com/>
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140116/7bd5b9a8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 53081 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140116/7bd5b9a8/attachment-0002.jpg>
More information about the Bldg-sim
mailing list