[Bldg-sim] NECB 2011 - Interpretation of 4.3.2.10

Genest, Frederic fgenest at pageaumorel.com
Wed Jul 9 14:21:55 PDT 2014


Hi Danielle.

Based on a proposed code change that's proposed for inclusion in NECB 2015, which clarify the description, this is what I understand it is :

-       "Personal control" => Full manual on/off control

-       "Occupancy-Sensing Mechanism - Manual" => Full manual on/off control (i.e. same as above)

-       "Occupancy-Sensing Mechanism - Automatic" => full auto on/off control

Other type of controls (bi-level, auto off/manual on) are not accounted for in NECB 2011 Section 4.3.

Regards,

[http://www.pageaumorel.com/signature/pma_sign.gif]

Frédéric Genest,


Pageau Morel et associés inc.


ing., M.Sc.A., PA LEED BD+C / Eng., M.A.Sc., LEED AP BD+C
ASHRAE HBDP
Chargé de projet / Project Manager
Associé / Associate
fgenest at pageaumorel.com<mailto:fgenest at pageaumorel.com>


210, boul. Crémazie O., bur. 110
Montréal (Québec) H2P 1C6
T 514.382.5150 (2203)
F 514.384.9872
www.pageaumorel.com<http://www.pageaumorel.com>


Poser un geste écolo : un engagement infini! Est-ce vraiment nécessaire d'imprimer ce courriel?
A green act: a commitment for infinity! Save trees. Print only when necessary.

AVERTISSEMENT CONCERNANT LA CONFIDENTIALITÉ / CONFIDENTIALITY MESSAGE
Ce courriel et toute information qui y est jointe sont confidentiels. Si vous avez reçu cette communication par erreur, veuillez nous en aviser immédiatement et effacer l'original, sans en tirer de copie ni en dévoiler le contenu. / This e-mail and any information enclosed are confidential. If you have received this message by error, please notify us immediately and delete the original without making a copy and without disclosing its content.




De : Evenson, Devin [mailto:DEvenson at hydro.mb.ca]
Envoyé : 9 juillet 2014 12:57
À : 'Krauel, Danielle'; bldg-sim at lists.onebuilding.org; IBPSA-GTA-L at listserv.utoronto.ca
Objet : Re: [Bldg-sim] NECB 2011 - Interpretation of 4.3.2.10

Hi Danielle -

I don't have a quick answer to your question but just to let you and other interested individuals know the Users' Guide  for the NECB 2011 is now available (released a couple weeks back) for purchase at the following link https://commerce-irc.nrc-cnrc.gc.ca/nrcb2c/b2c/display/(xcm=NRC-R3PITREX&layout=6_1_65_54_5_2&uiarea=2&ctype=areaDetails&carea=0000000064)/.do


Devin Evenson, P.Eng. CEM, CMVP
Manitoba Hydro | Customer Engineering Services
General Mail: PO Box 815 STN Mail | Winnipeg, MB | R3C 2P4
Courier: 6-360 Portage Ave | Winnipeg, MB | R3C 0G8
tel. 204-360-3971 | fax 204-360-6109
devenson at hydro.mb.ca<mailto:devenson at hydro.mb.ca>



From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Krauel, Danielle
Sent: Wednesday, July 09, 2014 11:02 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>; IBPSA-GTA-L at listserv.utoronto.ca<mailto:IBPSA-GTA-L at listserv.utoronto.ca>
Subject: [Bldg-sim] NECB 2011 - Interpretation of 4.3.2.10

Hello,

Quick question about the NECB 2011 (Section 4.3.2.10). There are different factors (credits to account for):

-          "Personal control"

-          "Occupancy-Sensing Mechanism - Manual"

-          "Occupancy-Sensing Mechanism - Automatic"

What is meant by each of these? I'm assuming:

-          Personal Control - An on/off switch or task light.

-          Occupancy-Sensing Mechanism - Manual: A push-button for an occupancy override with timer (no switch).

-          Occupancy-Sensing Mechanism - Automatic: An automatic occupancy sensor.

If anyone can confirm my interpretation is correct, that would be great. Thanks.

[cid:image005.jpg at 01CF9B98.CB16B130]Danielle Krauel, ing., P.Eng., LEED AP
Halsall Associates
Tel: 613.907.7540 * Toll Free: 1.877.442.5725 ext 286 * www.halsall.com<http://www.halsall.com/>
Vancouver * Calgary * Sudbury * Burlington * Toronto * Ottawa
Best Workplaces in Canada, Eight Consecutive Years: 2007-2014
_________________________
A Parsons Brinckerhoff Company


______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140709/40d2bbcf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 2843 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140709/40d2bbcf/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.gif
Type: image/gif
Size: 3890 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140709/40d2bbcf/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 2232 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140709/40d2bbcf/attachment.jpg>


More information about the Bldg-sim mailing list