A low energy radiant slab system is one of the strategies in Nrel's 'Strategies
for 50% energy savings in large offices'
<http://www.nrel.gov/docs/fy10osti/49213.pdf>. Worth a skim through!
Radiant systems such as chilled beams affect Operative temperature more
directly than VAV. The standard unmet hours test is therefore a little
unfair to these kinds of system. Perhaps it is worth the hassle
demonstrating that a comparable level of comfort is achieved during
occupied hours.
Apart from the conditioning of outdoor air latent heat removal is limited
because chilled water temperatures are higher. DOAS tends to deliver air at
a higher temperature as well - typically 15 - 16degC. This is also a
limiting factor in terms of the kind of load that CBs can deal with.
Designers are loath to specify CBs. Reasons include loss of flexibility for
subsequent fit outs, limited loads and limited contractor experience.
Hope this helps
Chris
On 10 Jun 2014 13:01, "David Eldridge" <DEldridge at grummanbutkus.com> wrote:
> 28% reduction sounds like a big difference if you are referring to total
> energy use of the building.
>
> Can you go back to your two cases and show each end-use to verify where
> the savings is occurring?
>
> DSE Mobile
>
> On Jun 10, 2014, at 1:46 AM, "Sanket Puranik" <sanketpuranik at gmail.com>
> wrote:
>
> Hi all,
>
> I have modeled chilled beams and conventional VAV systems for an office
> building. I am getting 28% lower annual energy consumption with chilled
> beams.
>
> Has anyone done similar comparison? I would like to confirm if such
> energy savings are achievable with chilled beams??
>
> Thanks and Regards,
> Sanket
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140611/9b81f058/attachment.htm>
More information about the Bldg-sim
mailing list