[Bldg-sim] Cooling Energy consumption in Winter
Brian Fountain
bfountain at greensim.com
Mon Mar 31 07:34:03 PDT 2014
Further to this, ensure your chilled water loop operation is not set to
Standby which will cause standby chiller losses all through the winter even
if there is no load. You can set the loop to Demand (only run when a
chilled water valve is open), Snap or Schedule it.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Duggin, Cory
Sent: Monday, March 31, 2014 10:20 AM
To: Attiq; bldg-sim at lists.onebuilding.org
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Cooling Energy consumption in Winter
Create an availability schedule that locks it out during the winter months.
The real question is why does it think you have a cooling load in the
winter.
Cory Duggin, EI
Energy Engineer I
TLC Engineering for Architecture
direct dial 615-346-1939
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Attiq
Sent: Monday, March 31, 2014 8:59 AM
To: bldg-sim at lists.onebuilding.org
Cc: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Cooling Energy consumption in Winter
Hi there,
I am modeling a VAV system in eQUEST. The designed system mechanical cooling
is shut off in the winter. The VAV system selection in eQUEST results in
winter mechanical cooling energy consumption. How can we model the
mechanical cooling to shut off in the winter. I have tried number ways with
no success. Help would be appreciated.
Thanks.
Attiq
Sent from my iPhone
> On Mar 24, 2014, at 4:03 PM,
<mailto:bldg-sim-request at lists.onebuilding.org>
bldg-sim-request at lists.onebuilding.org wrote:
>
> Send Bldg-sim mailing list submissions to
> <mailto:bldg-sim at lists.onebuilding.org> bldg-sim at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> <http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> <mailto:bldg-sim-request at lists.onebuilding.org>
bldg-sim-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> <mailto:bldg-sim-owner at lists.onebuilding.org>
bldg-sim-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
> Today's Topics:
>
> 1. Insulation and heat recovery prices (Rasheed Ahmad)
> 2. LBNL releases version 1.0.2 of EnergyPlusToFMU (Thierry Nouidui)
> <mime-attachment> <mime-attachment>
> _______________________________________________
> Bldg-sim mailing list
> <mailto:Bldg-sim at lists.onebuilding.org> Bldg-sim at lists.onebuilding.org
> <http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
_______________________________________________
Bldg-sim mailing list
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140331/972101e6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 9932 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140331/972101e6/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29623 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140331/972101e6/attachment-0005.png>
More information about the Bldg-sim
mailing list