[Bldg-sim] Cannot get Baseboard to work in New York
Madhav Munshi
mmunshi at kohlerronan.com
Wed Nov 19 08:44:36 PST 2014
John,
You would need to enter in the capacity of the baseboards for them to kick on.
MADHAV MUNSHI | BEMP, LEED AP BD+C
Kohler Ronan, LLC | www.kohlerronan.com<http://www.kohlerronan.com/>
mmunshi at kohlerronan.com<mailto:mmunshi at kohlerronan.com>
1370 Broadway, New York, NY 10018
212.695.2422 F 212.695.2423
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Wednesday, November 19, 2014 11:40 AM
To: bldg-sim at onebuilding.org
Subject: [Bldg-sim] Cannot get Baseboard to work in New York
Know I am missing something.
I have 4 floors of electric baseboards in New York City building. I have the rating blank and the CTRL on Thermostatic. It says if there is any heating, the baseboards should come on 1st. There IS heating, but no baseboards.
Help?
John