Julien.Dutel at mern.gouv.qc.ca
Julien.Dutel at mern.gouv.qc.ca
Fri Jun 19 12:52:36 PDT 2015
Hello,
Could sounds like stupids questions, but there's no such thing as a stupid question!
90.1 - 2013 interior lighting controls changed dramatically compare to the precedent version, not in substance but in form, I have questions about it.
Question 1)
In section 9.4.1.1(a) Local control, does "manual lighting controls" means Manual On AND Manual Off ?
The 2013 User Manual doesn't clearly answer this question. I wonder because there are others options called "restricted to Manual ON", "Automatic full OFF",etc.. so my logic would be to called Local control "Manual ON/ Manual OFF".
Question 2) (for a 90.1-2013 compliance)
For example, suppose a unique fixture of two T8 32W installed in an 20 m2 office enclosed by ceilingheight partitions. By reading Table 9.6.1, I would installed :
- a switch able to manual ON and manual OFF : for Local Control requirement (the manual OFF is the purpose of question 2)
- no automatic ON : to comply either Restricted to manual ON and Restricted to Partial Automatic ON
- a bilevel ballast and bilevel switch : for Bilevel Lighting control requirement
- no daylight control since the installed lighting power is under 150W
- a general lighting controller able to shutoff the light after business hour, for scheduled Shufoff option (the switch is able to override the scheduled shutoff for no more than 2hours)
Even if I have a scheduled Shufoff, does the local control requirement requires to have a Manual OFF ?
I think yes, so there will be energy savings during the business hours when the occupant leave the office and switch the light off manually, but the unclear "manual lighting controls" of Local Control requirement make me doubt of the Manual OFF requirement...!
Thanks,
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec) G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
http://www.efficaciteenergetique.mrn.gouv.qc.ca<http://www.efficaciteenergetique.mrn.gouv.qc.ca/>
AVIS DE CONFIDENTIALITÉ
Ce message est confidentiel. Il est à l'usage exclusif du destinataire ci-dessus. Si vous n'êtes pas le destinataire visé ou une personne autorisée à lui remettre cette communication, vous êtes par la présente avisé qu'il est expressément interdit de le diffuser, de le distribuer, de le reproduire, d'en dévoiler la teneur ou de prendre quelque mesure fondée sur l'information qui y est contenue. S'il vous a été envoyé par erreur, veuillez en informer immédiatement l'expéditeur par téléphone au 418 627-6379 et détruire ce message ainsi que toute copie de celui-ci.
P Devez-vous vraiment imprimer ce courriel? Si oui, pensez l'imprimer recto-verso!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150619/18fa2b29/attachment.htm>
More information about the Bldg-sim
mailing list