[Bldg-sim] What do people do about Leap Years? was Re: Energy model calibration - normalizing the utility bills to month start-end
Jim Dirkes
jim at buildingperformanceteam.com
Tue Jun 23 17:45:36 PDT 2015
Dear Joe,
Absolutely no condescension intended. I apologize for even coming close.
It was supposed to be tongue in cheek; I realize that switching software is
a tough thing and not necessarily a good plan for all.
On Tue, Jun 23, 2015 at 5:17 PM, James Hansen <jhansen at ghtltd.com> wrote:
> Getting upset that eQuest / DOE-2 doesn’t incorporate leap year data is
> like getting upset that it can’t predict a snow day. Or a power outage.
> If you are using an energy model for a specific task where missing 1 day in
> 1,460 is going to affect someone’s decision making process, and/or you’re
> not willing to multiply February energy consumption by 29/28 for that year,
> then that is worrisome. No energy modeling program is so accurate that
> this would make a difference. But that’s just my opinion. I have lots of
> scratches on my car and don’t care…
>
>
>
> -James
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Karen Walkerman
> *Sent:* Tuesday, June 23, 2015 4:57 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] What do people do about Leap Years? was Re:
> Energy model calibration - normalizing the utility bills to month start-end
>
>
>
> I hear your frustrations Joe, but after finding many, many issues with
> eQuest/Doe-2 that never got fixed, I eventually did "just" switch to
> EnergyPlus. I'm not sure when the last time DOE2 got a major update, but
> EnergyPlus is getting major updates all the time. There are people
> actively supporting this software and every bug and idiosyncrasy I've found
> has either been fixed, or is in the cue to be fixed.
>
>
>
> In my opinion, this community needs to either:
>
>
>
> 1. Support a major update to eQuest/DOE-2 that fixes this, and many other
> issues. If you are capable and interested in fixing some of these bugs -
> maybe try a crowdfunding campaign? People could contribute towards fixing
> particular issues or bugs.
>
> 2. Recognize the limitations of eQuest/ DOE-2 and use it only when
> projects can be appropriately modeled with this software.
>
> 3. Switch software packages completely.
>
>
>
> One of the challenges in this industry is that people are used to getting
> software for free. eQuest, DOE-2, EnergyPlus have all be developed in
> large part with public funding. When that funding goes away, support
> stops, but people still have the expectation that the software should be
> free.
>
>
>
> --
>
> Karen
>
>
>
> On Tue, Jun 23, 2015 at 4:43 PM, Joe Huang <
> yjhuang at whiteboxtechnologies.com> wrote:
>
> The responses so far are not what I expected and, in my view, miss the
> point.
> I was not talking about workarounds or ignoring the missing day in DOE-2,
> which is what I presume everyone has been doing up until now. I'm frankly
> tired of that, because adding the fixes to DOE-2 seems to be quite easy to
> do.
>
> I also find the responses of "just use EnergyPlus" to be disingenuous and
> condescending. It's like trying to fix a scratch on your car, and then
> somebody comes by and says, "oh, just go and buy this new better one".
>
> Joe
>
> Joe Huang
>
> White Box Technologies, Inc.
>
> 346 Rheem Blvd., Suite 205A
>
> Moraga CA 94556
>
> yjhuang at whiteboxtechnologies.com
>
> http://weather.whiteboxtechnologies.com for simulation-ready weather data
>
> (o) (925)388-0265
>
> (c) (510)928-2683
>
> "building energy simulations at your fingertips"
>
> On 6/23/2015 1:21 PM, Justin Spencer wrote:
>
> I think the cleanest is you just pretend every day is off by one. Ignore
> all of the month garbage (yes you'll be off by a day at times). Just think
> about it as days 1-365, with the right day of the week assigned. You can
> reassign your holidays if you want. You wind up dropping the real 12/31.
>
>
>
> But I like the "just use EnergyPlus" option.
>
>
>
> On Tue, Jun 23, 2015 at 12:57 PM, Jim Dirkes <
> jim at buildingperformanceteam.com> wrote:
>
>
> 1. Use EnergyPlus :), which allows >365 days. This is also helpful
> when the combined two-fuel billing cycle is 13-14 months.
> 2. Ignore the 1/365 difference. Do you really think it will matter
> much?
>
>
>
> On Tue, Jun 23, 2015 at 2:48 PM, Joe Huang <
> yjhuang at whiteboxtechnologies.com> wrote:
>
> This is a little off-topic, but something I've pondered for some time...
>
> The question is when people are using eQUEST/DOE-2 with historical year
> weather, what do you do when it's a leap year? Since DOE-2
> always simulates a 365-day year, do you just ignore the missing leap day,
> but then don't the Days of Week also get screwed up starting in March?
>
> Since a quarter of the years are leap years, I've never understood why
> accounting for them has been considered an insignificant detail.
> I mean, if I told you that a quarter of the time your simulation results
> would be a little wrong, isn't that a pretty high frequency?
>
> Many eQUEST/DOE-2 users also have the mistaken impression that the fault
> lies in the DOE-2 weather files, which is not true.
> Believe it or not, but the packed DOE-2 weather file format actually
> contains 384 days (32 days per month), and all the DOE-2 weather files I
> produce always contains Feb. 29 for the leap years (as well as other
> enhancements like greater precision in the data).
>
> So, where does the problem lie? It's in the clock within DOE-2 that
> always sets February to be 28 days. In other words, DOE-2 will read the
> weather file and do the simulation only through February 28th, even though
> the weather file contains data through February 32nd (:-)), although
> everything beyond the 28th would be blank on non-leap years, and beyond the
> 29th on leap years.
>
> When I've looked through the DOE-2.1E code, there are even flags setting
> the leap years but these are never used. I've thought many times of toying
> around with the code to see how difficult it would be to implement leap
> years, but just haven't gotten around to it. As far as I can see, the
> biggest difficulty might might have to do not with the simulation itself,
> but with the reporting.
>
> I'd like to know if others think this is something of sufficient
> importance to merit further investigation.
>
> Joe
>
>
> Joe Huang
>
> White Box Technologies, Inc.
>
> 346 Rheem Blvd., Suite 205A
>
> Moraga CA 94556
>
> yjhuang at whiteboxtechnologies.com
>
> http://weather.whiteboxtechnologies.com for simulation-ready weather data
>
> (o) (925)388-0265
>
> (c) (510)928-2683
>
> "building energy simulations at your fingertips"
>
> On 6/23/2015 10:27 AM, Collinge, William Overton wrote:
>
> All,
>
>
>
> This is a fantastic thread, and I am wondering if it could be taken one
> step further to query if anyone has experience with methods to attempt
> calibrating models of energy savings attributable to retrofits of multiple
> systems simultaneously (plant, envelope, HVAC etc. – as most real-world
> retrofits likely are), going past the 4- or 5-parameter breakpoint
> regression models to incorporate inverse modeling of specific load types
> and their space- or time-variable characteristics. This would fit under
> multivariate methods in the last line of Table 2 in the older version of
> ASHRAE Guideline 14 that Jeff Haberl has posted on his website, and would
> attempt to standardize Maria’s Step 5 below without (possibly) the need to
> conduct as much in-depth field verification as might otherwise be required.
> I’ve dabbled in this a little bit…without extensive discussions with others…
>
>
>
> Example: changing the OA ventilation rate is going to have a specific load
> profile versus some retrofit that affects the solar gain rate. Of course,
> much easier in theory to do calibrations of this sort with hourly meter
> data versus monthly utility bills…
>
>
>
> Bill Collinge
>
> Postdoctoral Scholar
>
> University of Pittsburgh
>
> Department of Civil and Environmental Engineering
>
>
>
>
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
> <bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of *Maria Karpman
> *Sent:* Tuesday, June 23, 2015 12:02 PM
> *To:* 'Jeff Haberl'; 'Joe Huang'; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy model calibration - normalizing the
> utility bills to month start-end
>
>
>
> Hello all,
>
>
>
> We usually do the following to calibrate model to monthly utility bills:
>
> 1) Create or purchase weather file corresponding to pre-retrofit
> period for which we have billing data. Lately we’ve been using
> WeatherAnalytics files, which we found to be more cost effective than
> creating our own (they charge $40 for an annual file).
>
> 2) Run simulation using this weather file instead of TMY.
>
> 3) Standard simulation reports (we typically use eQUEST) show usage
> by calendar month (e.g. January, February, etc.) which is usually not
> aligned with dates of utility bills, as noted in the question that started
> this thread. As Brian mentioned in one of the earlier posts, this may be
> circumvented by entering the actual meter read dates into eQUEST as shown
> in the screenshot below. This will align usages shown in eQUEST’s “E*”
> reports such as ES-E with the actual utility bills. The approach does not
> allow entering more than one read date per month (e.g. we can’t capture
> April 3 – 28 bill). For projects where this limitation is an issue we
> generate hourly reports that show consumption by end use for each meter in
> the project, and aggregate it into periods that are aligned with utility
> bills.
>
> [image: cid:image001.png at 01D0ADD6.D9D5F9F0]
>
>
>
> 4) We then copy simulation outputs (either from ES-E or hourly
> reports, depending on the method used) into a standard spreadsheet with
> utility data. The spreadsheet is set up to plot side by side monthly
> utility bills and simulated usage, and also calculates normalized mean bias
> error (NMBE) and variance CV(RMSE).
>
> 5) If we did not to where we want to be with NMBE and CV(RMSE) we
> adjust and re-run the model, and re-paste results into the same
> spreadsheet.
>
>
>
> In my experience regression analysis using weather as independent variable
> (i.e. running model with TMY file and normalizing for difference in
> weather) or relying on HDD to allocate usage to billing periods can be very
> misleading, mainly because on many projects weather is not the main driver
> of consumption. For example energy usage of a school during a given time
> period depends much more on vacation schedule than outdoor dry bulb
> temperatures.
>
>
>
> Thanks,
>
>
>
> --
>
> *Maria Karpman *LEED AP, BEMP, CEM
>
> ________________
>
> Karpman Consulting
>
> www.karpmanconsulting.net
>
> Phone 860.430.1909
>
> 41C New London Turnpike
>
> Glastonbury, CT 06033
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
> <bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of *Jeff Haberl
> *Sent:* Tuesday, June 23, 2015 10:16 AM
> *To:* Joe Huang; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy model calibration - normalizing the
> utility bills to month start-end
>
>
>
> Hello Joe,
>
>
>
> Yes, you can count the degree days and regress against that to show a
> correlation. However, one will get a better "fit" to the weather data if
> you regress to the degree day that is calculated for the balance point
> temperature of the building -- hence the inverse model toolkit or the
> variable based degree day method.
>
>
>
> PRISM actually calculates the degree days to a variety of change points
> and actually provides a table for each location that you use as a look up.
> The IMT will actually perform a variable based degree day calculation that
> agrees well with PRISM. IMT will also provide you with the average daily
> temperature for the billing period.
>
>
>
> When using DOE-2 for actual billing periods, one will have to extract the
> appropriate hourly variable, sum it to daily and then regroup to align with
> the billing periods. Here's a chunk of code that will create a dummy plant,
> display PV-A, PS-A, PS-E and BEPS, and extract the relevant hourly
> variables to normalize the BEPS to the utility bills:
>
>
>
> INPUT PLANT ..
>
>
>
> PLANT-REPORT VERIFICATION = (PV-A)
>
> $ PV-A, EQUIPMENT SIZES
>
>
>
> SUMMARY = (PS-A,PS-E,BEPS)
>
>
>
> $ PS-A, PLANT ENERGY UTILIZATION SUMMARY
>
> $ PS-E, MONTHLY ENERGY END USE SUMMARY
>
> $ BEPS, BUILDING ENERGY PERFORMANCE SUMMARY
>
>
>
> HVAC=PLANT-ASSIGNMENT ..
>
>
>
> $ EQUIPMENT DESCRIPTION
>
> $ ELECTRIC DOMESTIC WATER HEATER
>
>
>
> BOIL-1 =PLANT-EQUIPMENT TYPE=ELEC-DHW-HEATER SIZE=-999 ..
>
>
>
> $ ELECTRIC HOT-WATER BOILER
>
>
>
> BOIL-2 =PLANT-EQUIPMENT TYPE=ELEC-HW-BOILER SIZE=-999 ..
>
>
>
> $ HERMETICALLY SEALED CENT CHILLER
>
>
>
> CHIL-1 =PLANT-EQUIPMENT TYPE=HERM-CENT-CHLR SIZE=-999 ..
>
>
>
> $ Graphics block for Data Processing ***
>
>
>
> RP-3 = SCHEDULE THRU DEC 31 (ALL) (1,24) (1) ..
>
>
>
> $ 8 = Total PLANT heating load (Btu/h)
>
> $ 9 = Total PLANT cooling load (Btu/h)
>
> $ 10 = Total PLANT electric load (Btu/h)
>
>
>
> BLOCK-3-1 = REPORT-BLOCK
>
> VARIABLE-TYPE = PLANT
>
> VARIABLE-LIST = (8,9,10) ..
>
> BLOCK-3-2 = REPORT-BLOCK
>
> VARIABLE-TYPE = GLOBAL
>
> VARIABLE-LIST = (1) ..
>
> HR-3 = HOURLY-REPORT
>
> REPORT-SCHEDULE = RP-3
>
> REPORT-BLOCK = (BLOCK-3-1,BLOCK-3-2) ..
>
>
>
> END ..
>
>
>
> COMPUTE PLANT ..
>
>
>
> STOP ..
>
>
>
> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?
> Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu
> <........jhaberl at tamu.edu>
> Professor........................................................................Office
> Ph: 979-845-6507
> Department of Architecture............................................Lab
> Ph:979-845-6065
> Energy Systems Laboratory...........................................FAX:
> 979-862-2457
> Texas A&M
> University...................................................77843-3581
> College Station, Texas, USA, 77843.............................
> http://esl.tamu.edu
> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) 8=0
> ------------------------------
>
> *From:* Bldg-sim [bldg-sim-bounces at lists.onebuilding.org] on behalf of
> Joe Huang [yjhuang at whiteboxtechnologies.com]
> *Sent:* Monday, June 22, 2015 9:17 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy model calibration - normalizing the
> utility bills to month start-end
>
> Maybe I'm missing something here, but why can't you just count up the
> degree days for the utility period?
> I hope you're not working with average or "typical year" degree days, but
> the degree days from the same time period.
>
> I also recall that the old Princeton Scorekeeping Method (PRISM) back in
> the 1980's allows the user to enter the degree days for that time period,
> so it's not a new problem.
>
> Joe
>
> Joe Huang
>
> White Box Technologies, Inc.
>
> 346 Rheem Blvd., Suite 205A
>
> Moraga CA 94556
>
> yjhuang at whiteboxtechnologies.com
>
> http://weather.whiteboxtechnologies.com for simulation-ready weather data
>
> (o) (925)388-0265
>
> (c) (510)928-2683
>
> "building energy simulations at your fingertips"
>
> On 6/22/2015 6:09 AM, Jones, Christopher wrote:
>
> When calibrating an energy model to utility bills the utility bills
> often don’t align with the month start and end. I have reviewed a couple
> methods to calendar normalize the utility bills but find them somewhat
> unsatisfactory.
>
>
>
> For example the method I am looking at does the following:
>
> The April gas bill runs from March 25 – April 24. The algorithm takes the
> average number of m3 per day from that bill, applies it to the days in
> April. Then it takes the average number of days from the May bill which
> runs from April 24 – May 25 and applies that average to the remaining days
> in April.
>
>
>
> The issue is that the March-April period has much higher HDD than the
> April-May period and the “normalized” gas usage is significantly lower than
> the simulation data for April.
>
>
>
> I am wondering if there are any papers or other sources of information as
> to how others approach this problem.
>
>
>
>
>
> [image: cid:image003.png at 01D09C46.E75BA0D0]
>
> *Christopher Jones,*P.Eng.
> Senior Engineer
>
>
>
> *WSP Canada Inc.*
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4
> T +1 416-644-4226
>
> F +1 416-487-9766
>
> C +1 416-697-0065
>
>
>
> www.wspgroup.com
>
>
> ------------------------------
>
>
> You are receiving this communication because you are listed as a current
> WSP contact. Should you have any questions regarding WSP’s electronic
> communications policy, please consult our Anti-Spam Commitment
> www.wspgroup.com/casl
> <https://teesmail.tees.tamus.edu/owa/UrlBlockedError.aspx>. For any
> concern or if you believe you should not be receiving this message, please
> forward this message to us at caslcompliance at wspgroup.com so that we can
> promptly address your request. This message is intended only for the use of
> the individual or entity to which it is addressed, and may contain
> information which is privileged, confidential, proprietary or exempt from
> disclosure under applicable law. If you are not the intended recipient or
> the person responsible for delivering the message to the intended
> recipient, you are strictly prohibited from disclosing, distributing,
> copying or in any way using this message. If you have received this
> communication in error, please notify the sender, and destroy and delete
> any copies you may have received.
>
> WSP provides professional land surveying services through the following
> entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
> Partnership
>
>
>
> _______________________________________________
>
> Bldg-sim mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ------------------------------
>
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2014.0.4800 / Virus Database: 4365/10055 - Release Date: 06/19/15
>
>
>
> _______________________________________________
>
> Bldg-sim mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653
> jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteamcom>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413>
>
> Studies show that four out of every three people have a hard time with
> math.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> ------------------------------
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee. It is the
> property of GHT Limited. Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful. If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments. Thank you.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
Studies show that four out of every three people have a hard time with
math.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150623/d4990be6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 9286 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150623/d4990be6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 152476 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150623/d4990be6/attachment-0001.png>
More information about the Bldg-sim
mailing list