[Bldg-sim] Use of simulation for ASHRAE 62.1 for compliance.
Nathan Miller
nathanm at rushingco.com
Fri Mar 20 06:16:55 PDT 2015
Hema,
It’s been a while since I documented a natural ventilation project for LEED (I’m assuming you are doing this for LEED?), but in the past (LEED-NC v2.2 era), I’ve used annual natural ventilation simulation results (TAS and IES Virtual Environment are a couple of tools that work) to show that both peak and typical natural ventilation air flow rates are SIGNIFICANTLY higher than the requirements if the building used a mechanical ventilation scheme. My impression of CFD is that it is more of a snap-shot in time rather than giving you results across a time-period, so maybe you could demonstrate flow on a peak day and maybe a “stagnant” day to help present your design. Otherwise I’d recommend presenting results from an annual (or natural-ventilation-season) simulation.
Maybe people who have submitted nat vent designs for review in the more recent past can provide more insight.
Sincerely,
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hema Sree Rallapalli
Sent: Friday, March 20, 2015 2:33 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Use of simulation for ASHRAE 62.1 for compliance.
Dear All,
We are working on a project where we want to make the building naturally ventilated as per ASHRAE 62.1-2007
The prescriptive requirements for natural ventilation are as follows:
* Naturally ventilated spaces must be permanently open to and within 25 ft (8 m) of operable wall or roof openings to the outdoors, the openable area of which is a minimum of 4% of the net occupiable floor area being naturally ventilated. (The net occupiable floor area is measured from the inside surfaces of the walls, excluding permanently enclosed obstructions such as shafts and columns.
* Where interior spaces without direct openings to the outdoors are ventilated through adjoining rooms, the opening between rooms must be permanently unobstructed and have a free area of not less than 8% of the area of the interior room nor less than 25 ft² (2.3 m²).
We have square floor plate of 1000 square meter. As per ASHRAE 62.1 only the perimeter area with a depth of 8 meter can be considered as naturally ventilated space. But we have designed the windows and positioned the windows in order to encourage cross ventilation and we can show sufficient distribution of air by doing CFD simulations. Are the CFD simulations enough to prove that this building is compliant with ASHRAE 62.1 as a naturally ventilated building?
Thanks for your time.
Hema.