The intention to always require heating in the base case is to prevent people from
claiming energy savings simply by not providing any space conditioning! However, if your
building and climate makes heating unnecessary, that should show up in your base case
simulations where the heating system never comes on. You should still use a reasonable
heating schedule, e.g., 21 C (70F) during the day and 18.3C (65F) at night (or maybe even
15.6C (60F) if building is unoccupied), just to prove that heating is indeed unnecessary.
You might also track the indoor temperatures of your proposed building to convince LEED
reviewers that indoor temperatures are always above the comfort zone.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 3/26/2015 12:16 AM, Rathna Shree wrote:
> Thank you Joe Huang. I am using Equest for the simulation. Can we set the heating as not
> installed for LEED submissions?
>
>
>
> On Wednesday, 25 March 2015 11:59 PM, Joe Huang <yjhuang at whiteboxtechnologies.com> wrote:
>
>
> It all depends on which simulation program you're using, but all of them should be able
> to accommodate you very easily. You can either set the Heating Schedule to be never on,
> and the Heating Setpoint Temperature to something very low, like 10 C (50 F).
>
> Joe
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com
> http://weather.whiteboxtechnologies.com for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
> On 3/25/2015 2:58 AM, Rathna Shree wrote:
>> Dear All,
>>
>> In few of the climatic conditions we work on doesn't require heating at all. The
>> temperature might go little less than 20deg C in winter but heating will definitely not
>> be installed in the project. For these projects, how do we set the heating set point
>> temperatures so that heating never switches on. we are facing issues especially while
>> modelling VAV with PFP boxes in equest (PIU systems). The base case and proposed case
>> heating and fan energy consumption are highly affecting the final savings results. I am
>> looking to avoid this scenario and ensure heating never switches on, therefore zone
>> fans also do not work.
>>
>> Please guide.
>>
>> Regards,
>> Rathnashree
>>
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150326/f600bb11/attachment.htm>
More information about the Bldg-sim
mailing list