[Bldg-sim] VRF performance curve

Duggin, Cory Cory.Duggin at tlc-eng.com
Wed May 27 06:13:29 PDT 2015


I would either use a WSHP or a chilled water system with 0 pumping energy.

Cory Duggin, PE, LEED AP BD+C
Associate/Energy Engineer
TLC Engineering for Architecture
direct:

615-346-1939



From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rathna Shree
Sent: Wednesday, May 27, 2015 2:18 AM
To: BldgSim Mailing List; equest-users at onebuilding.org
Subject: [Bldg-sim] VRF performance curve

Dear All,

I worked on a couple of projects in equest  using the VRF performance curves from Daikin and LG. The methodology i followed is as below:

1) Modelled packaged VAV with minimum flow ratio 1.
2) Created systems based on number of ODU's and assigned multiple zones to the respective ODU. (Just like modelling a AHU)
3) Inputted the ODU Cooling capacity and supply flow
4) Fans will be constant volume.
5) Since it is a cooling only system, i assigned only the "Cool EIR - fEWB-OAT", "Cool-EIR-fPLR" and "Cool cap-fEWB&OAT" curves. Rest were all default DX unit curves.

 PVAV system is used as PSZ system cannot handle multiple zones well thus causing unmet hours.

I did 2 trials, one with default DX curves and the other with performance curves from LG and Daikin. The results showed a decrease in cooling energy consumption by more than 30% thus impacting the overall energy consumption by more than 10%.

Is the simulation methodology and results appropriate? I feel the savings is on a higher side.

Please advise.

Regards,
Rathnashree