[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] DX Coils



Greetings,

RE: input for Coil:DX:CoolingBypassFactorEmpirical

Has anyone generated Part Load Fraction Correlation functions for larger
industrial rooftop package units?  It seems difficult to get part load data
for specific models.   All I have been able to come up with is to generate a
suitable cubic from the Part_Load Factor Curve provided as Figure 1. in ARI
Standard 340/360-2000.  This seems to work but I am not sure if this is the
way to go since it often goes way below the E+ limit of 0.7.  Also I can't
seem to push the SHR higher than 0.75 which is less than what is indicated
by the equipment specs I am using.  

Any ideas?  Thanks in advance.  

Brent Griffith

------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/