[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Slab Programme



Can the Slab Program be used with crawl spaces and a
combination of a crawl space and slab on the ground
floor?

--- "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> Answers regarding questions about inputs to the slab
> program 
> (\EnergyPlus\PreProcess\GrndTempCalc\slab.exe):  
> 
> > Surface Albedo: NO Snow/Snow? 
> 
> This will change the ground surface temperature by
> reflecting solar 
> energy.  The Albedo is more commonly recorded than
> the absorptivity.  
> The albedo can range from as low as 0.05 for
> blacktop surfaces to 
> 0.95 for fresh snow.  Representative average values
> for North America 
> are 0.16 in the summer and 0.40 in the winter.  
> Ref:  Sellers, 
> Physical Climatology, Univ of Chicago Press, 1965(
> from W. P. 
> Bahnfleth, Ph.D. Thesis, University of Illinois,
> Mech Eng Dept, 
> Urbana, IL, 1989)  
> 
> 
> 
> > Under slab insulation: What does such a insulation
> look like as
> > the next field in the object depicts the width of
> strip of
> > insulation. 
> 
> This is a layer of horizontal insulation of the
> width and thermal 
> resistance specified underneath the slab all around
> the perimeter.  
> 
> 
> > The area to perimeter ratio for this slab: this
> term is
> > self-explaining, but in the example idf-File
> > (Slab2x2VertInsMplsAP10) this ratio is 10- the
> specified dimension
> > of this slab is 12x12.  
> 
> The example uses the EquivSlab and EquivAutoGrid
> options.  Thus the 
> input in the AutoGrid object is not used.  The A/P
> ratio of 10 is 
> used.  
> 
> 
> > Thickness of slab on grade? 
> 
> This specifies the floor slab thickness.  It is used
> in conjunction 
> with the "Slab k" field to determine the thermal
> resistance of the 
> slab.  This and the specified temperatures and heat
> transfer 
> coefficients can be used to estimate the monthly
> heat flux through 
> the slab.  
> 
> 
> > Distance from edge of slab to domain edge? 
> 
> This value is what is used to set up the grid for
> the 
> multidimensional calculation.  It should be far
> enough from the slab 
> to be in an undisturbed ground temperature.   15
> meters is quite 
> reasonable.  
> 
> 
> 
> 
> 
> 
> On 4 Oct 2002, at 13:32,
> alexander.beisteiner@fh-pinka wrote:
> 
> > Dear Sir/Madam
> > Using the programme Slab for calculating the
> ground temperature I
> > would need some help creating the IDF. Some fields
> in the various
> > objects are unclear to me:
> > 
> > Surface Albedo: NO Snow/Snow?
> > 
> > Under slab insulation: What does such a insulation
> look like as the
> > next field in the object depicts the width of
> strip of insulation.
> > 
> > The area to perimeter ratio for this slab: this
> term is
> > self-explaining, but in the example idf-File
> (Slab2x2VertInsMplsAP10)
> > this ratio is 10- the specified dimension of this
> slab is 12x12.
> > 
> > Thickness of slab on grade?
> > 
> > Distance from edge of slab to domain edge?
> > 
> > I am looking forward to your help.
> > Kind Regards
> > 
> > 
> > ----------------------------------------------
> > Alexander Beisteiner
> > Forschungs- und Technologietransfer
> > Pinkafeld GmbH
> > Steinamangerstrasse 21
> > 7423 Pinkafeld
> > 
> > Tel.: 0043/3357/45370-1324
> > alexander.beisteiner@xxxxxxxxxxxxxxxxxx
> > http://www.fh-pinkafeld.ac.at
> > 
> 
> 
> 
>
========================================================
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 


__________________________________________________
Do you Yahoo!?
Y! Web Hosting - Let the expert host your web site
http://webhosting.yahoo.com/

------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/