[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Effect of minimal HVAC loads on simulation results



So my understanding of what you said is that when HVAC loads are 
minimized the quality of construction and quality of installation 
become very important to the simulation program - does EnergyPlus 
have the capability to take these into consideration?

Thanks again -

Hailey


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> Hailey:
> 
> There is no implicit accuracy problem in the simulation for 
buildings 
> with low HVAC loads.  The primary issue for such buildings is that 
> the results become very sensitive to the building envelope and 
> internal gain characteristics.  Envelope U-values as-built are 
often 
> not as specified and infiltration is highly variable.  If trying to 
> match the performance of an existing building, it may be necessary 
to 
> measure the building's actual properties.  If trying to evalute a 
new 
> design, several cases should be run to try and bound the problem 
> using reasonable high and low values for parameters which are not 
> known precisely.  
> 
> Mike
> 
> 
> On 3 Jul 2003, at 0:58, c_l_hailey wrote:
> 
> > I have been doing some research into the accuracy of simulation 
> > programs on more innovative buildings.  Particularly, well-build
> > residential buildings with A LOT of passive solar design 
incorporated,
> > therefore requiring a minimal amount of mechanical HVAC.  These
> > simulations seem to have exceptionally high margin of error when
> > compared to theactual energy consumption.  Do you know if there 
is any
> > relationship?  Does EnergyPlus not respond well to buildings with 
a
> > HVAC system which only consumes say 30% of the structures 
energy?  
> > 
> > BTW - I am not very experienced with modeling, so I cannot tell 
you if
> > there is error in the inputs of the models I am looking at.
> > 
> > Thanks
> > 
> > Hailey
> > 
> > 
> > ------------------------ Yahoo! Groups Sponsor
> > ---------------------~--> Get A Free Psychic Reading! Your Online
> > Answer To Life's Important Questions.
> > http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
> > ------------------------------------------------------------------
---~
> > ->
> > 
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> > 
> > 
> > 
> > 
> > 
> > 
> > Your use of Yahoo! Groups is subject to
> > http://docs.yahoo.com/info/terms/ 
> > 
> 
> 
> 
> ========================================================
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/