[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: If there's no surface between two zones.



If all we're interested in is the eat exchange between the two, is 
it plausible to add a very thin "wall" with a very high thermal 
conductivity? That would seem to take care of the heat exchange 
issue. 

K-

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> You are correct.  If there is no surface defined, there will be no 
> exchange between the two zones.  CROSS MIXING is a good solution 
for 
> this case.  The difficult thing it to determine what the flow rate 
> should be for CROSS MIXING.  I would recommend trying a range of 
> values to determine how sensitive the results are to this value.
> 
> I do not know of a way to model an air curtain in EnergyPlus.
> 
> Mike
> 
> 
> On 23 Jul 2003, at 20:46, waspoorboy wrote:
> 
> > For example, a shopping mall has two HVAC systems. One serves the
> > north half of the mall, the other serves the south half of the 
mall.
> > The two control thermostats, one in the north zone, the other in 
the
> > south zone, respectively. There is actually no surface between 
the
> > north and south zone. If I didn't define a surface between two 
zones,
> > EnergyPlus will assume no heat transfer between the two zones, 
am I
> > correct ? In the real mall, however, there will be heat transfer
> > between the north and south zone. Is CROSS MIXING the typical 
solution
> > to this ?
> > 
> > If the main entrance of the mall has air curtain, can I model 
the air
> > curtain in EnergyPlus ? Thanks a lot.
> > 
> > 
> > ------------------------ Yahoo! Groups Sponsor
> > ---------------------~--> Buy Breakthrough Natural Health 
Specialties
> > at VitaminBoost.com $20 to $40 Naturally Painless Spray, Coral
> > Calcium, No Snore, EZ Appetite Suppressant.
> > http://www.challengerone.com/t/l.asp?cid=2882
> > http://us.click.yahoo.com/yoMABA/ruYGAA/ySSFAA/dkFolB/TM
> > -----------------------------------------------------------------
----~
> > ->
> > 
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> > 
> > 
> > 
> > 
> > 
> > 
> > Your use of Yahoo! Groups is subject to
> > http://docs.yahoo.com/info/terms/ 
> > 
> 
> 
> 
> ========================================================
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/