RE: [EnergyPlus_Support] Return Fan



Problem solved, thank you.
Sam Roose

	-----Original Message----- 
	From: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
	Sent: Fri 29/08/2003 6:55 a.m. 
	To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
	Cc: 
	Subject: Re: [EnergyPlus_Support] Return Fan
	
	
	The return fan is placed as the first component on the main branch of 
	the air loop, right before the outside air system.  I will upload an 
	example with return fan shortly into the Examples folder in the yahoo 
	files area.
	
	Mike
	
	
	On 28 Aug 2003, at 21:00, Samuel Roose wrote:
	
	> I am puzzled about how to specify return air fans as part of an air
	> loop. The attached file is an attempt at this based on Figure 43 of
	> the Input - Output reference. The intention is to flow through the
	> outside air system to supply fans, cooling coil, humidifier, zone and
	> then return the air back to the outside air system somehow. The file
	> runs fine without the return fans. Has anyone had any success with
	> return air fans? If so, please peruse the file (particularly the main
	> air loop branch and fans input). I would appreciate any feedback.
	> Thanks, Sam Roose Victoria University of Wellington
	> 
	> 
	> [Non-text portions of this message have been removed]
	> 
	> 
	> ------------------------ Yahoo! Groups Sponsor
	> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
	> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
	> $50 or more to the US & Canada.
	> http://www.c1tracking.com/l.asp?cid=5511
	> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
	> ---------------------------------------------------------------------~
	> ->
	> 
	> To unsubscribe from this group, send an email to:
	> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
	> 
	> The primary EnergyPlus web site is found at:
	> http://www.energyplus.gov
	> 
	> The group web site is:
	> http://groups.yahoo.com/group/EnergyPlus_Support/
	> 
	> Attachments are not allowed -- please post any files to the
	> appropriate folder in the Files are of the Support Web Site.
	> 
	> 
	> 
	> 
	> 
	> 
	> Your use of Yahoo! Groups is subject to
	> http://docs.yahoo.com/info/terms/ 
	> 
	
	
	
	========================================================
	Michael J. Witte, GARD Analytics, Inc.
	EnergyPlus Testing and Support      
	EnergyPlus-Support@xxxxxxxx
	
	
	
Yahoo! Groups Sponsor	
ADVERTISEMENT
Click Here! <http://rd.yahoo.com/M=244522.3707890.4968055.1261774/D=egroupweb/S=1705007389:HM/A=1595055/R=0/SIG=124j83ehr/*http://ashnin.com/clk/muryutaitakenattogyo?YH=3707890&yhad=1595055> 	
 <http://us.adserver.yahoo.com/l?M=244522.3707890.4968055.1261774/D=egroupmail/S=:HM/A=1595055/rand=821659031> 	

	To unsubscribe from this group, send an email to:
	EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
	
	The primary EnergyPlus web site is found at:
	http://www.energyplus.gov
	
	The group web site is:
	http://groups.yahoo.com/group/EnergyPlus_Support/
	
	Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
	
	
	
	
	
	
	Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 
	


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/