[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Question about design evaporative volumetric water flow rate



For the 6 smaller chillers, use 45.5 L/s for the design evaporator 
flow rate.  Assuming the chillers will operate in parallel, then the 
total chilled water loop flow rate will be 273 L/s.

Mike


On 18 Sep 2003, at 3:10, leeslwong wrote:

> Dear all,
> 
> After simulation the autosizing of an A/C building, which is 6300 kW
> of total cooling capacity. I propose to use 6 nos of 1050 kW of
> chiller for the building. The total evaporative water flow rate is 273
> L/s and the individual chilled water flow rate of 6 nos. of chiller is
> 45.5 L/s. I an planning to input 6 nos of CHILLER:ELECTRIC, which is
> 1050 kW for each chiller for the new input file. I wonder if someone
> could tell me 273 L/s or 45.5 L/s of Design Evaporator Volumetric
> Water Flow Rate {m3/s} should be used for each chiller?
> 
> Thanks
> 
> lee 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Upgrade to 128-Bit SSL Security!
> http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/