[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Economizer in Dual Duct VAV system doesn't work?



Hello, everyone:

I am trying to build a Dual Duct VAV System in
Energy-Plus. What I do is to modify the example idf
file in the E+ example directory and add an
economizer. Unfortunately, the economizer doesn?t
work. I have been blocked by this issue for more
than one week. Does anyone have some idea to solve
the problem? Thanks a lot.

The attached text file is part of my E+ system model.
Please let me know if you need more information or
the complete idf file.

Lei Zhou


======================================

NODE LIST,
    Supply Fan Inlet Temp Nodes,  !- Node List Name
    Supply Fan Inlet Node;   !- Node_ID_1
    
!-   ===========  ALL OBJECTS IN CLASS: BRANCH LIST ===========

BRANCH LIST,
    Dual Duct Air Loop Branches,  !- Branch List Name
    Air Loop Main Branch,    !- Branch Name 1
    Heating Coil Air Sys Branch,  !- Branch Name 2
    Cooling Coil Air Sys Branch,  !- Branch Name 3
    Return Air Loop Branch;  !- Branch Name 4

BRANCH LIST,
    Cooling Supply Side Branches,  !- Branch List Name
    CW Pump Branch,          !- Branch Name 1
    Big Chiller Branch,      !- Branch Name 2
    Supply Bypass Branch,    !- Branch Name 3
    Cooling Supply Outlet;   !- Branch Name 4

!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========

BRANCH,
    Air Loop Main Branch,    !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    OUTSIDE AIR SYSTEM,      !- Comp1 Type
    OA System 1,             !- Comp1 Name
    Return Fan Outlet Node,  !- Comp1 Inlet Node Name
    Supply Fan Inlet Node,   !- Comp1 Outlet Node Name
    PASSIVE,                 !- Comp1 Branch Control Type
    FAN:SIMPLE:ConstVolume,  !- Comp2 Type
    Supply Fan 1,            !- Comp2 Name
    Supply Fan Inlet Node,   !- Comp2 Inlet Node Name
    Supply Fan Outlet Node,  !- Comp2 Outlet Node Name
    PASSIVE;                 !- Comp2 Branch Control Type

BRANCH,
    Return Air Loop Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    FAN:SIMPLE:ConstVolume,  !- Comp1 Type
    Return Fan 1,            !- Comp1 Name
    Return Air Mixer Outlet, !- Comp1 Inlet Node Name
    Return Fan Outlet Node,  !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type

BRANCH,
    Heating Coil Air Sys Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleHeating,!- Comp1 Type
    Main Heating Coil,       !- Comp1 Name
    Heating Coil Inlet Node, !- Comp1 Inlet Node Name
    Heating Coil Outlet Node,!- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type

BRANCH,
    Cooling Coil Air Sys Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleCooling,!- Comp1 Type
    Simple Cooling Coil,     !- Comp1 Name
    Cooling Coil Inlet Node, !- Comp1 Inlet Node Name
    Cooling Coil Outlet Node,!- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type



!-   ===========  ALL OBJECTS IN CLASS: AIR PRIMARY LOOP ===========

AIR PRIMARY LOOP,
    Main Dual Duct Air Loop, !- Primary Air Loop Name
    Dual Duct System 1 Controllers,  !- Name: Controller List
    Dual Duct System 1 Schedule List,  !- Name: System Availability Manager
List
    autosize,                !- Primary air design volumetric flow rate {m3/s}
    Dual Duct Air Loop Branches,  !- Air Loop Branch List Name
    Dual Duct Connectors,    !- Air Loop Connector List Name
    Return Fan Outlet Node,  !- ReturnAir AirLoop Inlet Node
    Return Air Mixer Outlet, !- ZoneEquipGroup Outlet Node
    Zone Equipment Inlet Node List,  !- SupplyAirPath ZoneEquipGroup Inlet
Nodes
    Air Loop Outlet Node List;  !- AirLoop Outlet Nodes


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER LIST ===========

CONTROLLER LIST,
    Dual Duct System 1 Controllers,  !- Name
    Controller:Simple,       !- Controller Type 1
    Main Cooling Coil Controller,  !- Controller Name 1
    Controller:Simple,       !- Controller Type 2
    Main Heating Coil Controller;  !- Controller Name 2

CONTROLLER LIST,
    OA System 1 Controller,  !- Name
    CONTROLLER:OUTSIDE AIR,  !- Controller Type 1
    OA Controler 1;          !- Controller Name 1

!-   ===========  ALL OBJECTS IN CLASS: AIR LOOP EQUIPMENT LIST ===========

AIR LOOP EQUIPMENT LIST,
    OA System 1 Equipment,   !- Name
    OUTSIDE AIR MIXER,       !- KEY--System Component 1
    OA Mixing Box 1;         !- Component Name 1


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR SYSTEM ===========

OUTSIDE AIR SYSTEM,
    OA System 1,             !- Name
    OA System 1 Controller,  !- Name: Controller List
    OA System 1 Equipment,   !- Name of an Air Loop Equipment List
    VAV Sys 1 Avail List;    !- Name of a System Availability Manager List


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR INLET NODE LIST ===========

OUTSIDE AIR INLET NODE LIST,
    OA Inlet Node 1;         !- 1st Node name or node list name


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR MIXER ===========

OUTSIDE AIR MIXER,
    OA Mixing Box 1,         !- Name
    Supply Fan Inlet Node,   !- Mixed_Air_Node
    Outside Air Inlet Node 1,!- Outside_Air_Stream_Node
    Relief Air Outlet Node 1,!- Relief_Air_Stream_Node
    Return Fan Outlet Node;  !- Return_Air_Stream_Node

!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER LIST
===========

SYSTEM AVAILABILITY MANAGER LIST,
    VAV Sys 1 Avail List,    !- Name
    SYSTEM AVAILABILITY MANAGER:SCHEDULED,  !- System Availability Manager type
1
    VAV Sys 1 Avail;         !- System Availability Manager name 1

SYSTEM AVAILABILITY MANAGER LIST,
    Dual Duct System 1 Schedule List,  !- Name
    SYSTEM AVAILABILITY MANAGER:SCHEDULED,  !- System Availability Manager type
1
    Dual Duct System 1 Schedule;  !- System Availability Manager name 1


!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER:SCHEDULED
===========

SYSTEM AVAILABILITY MANAGER:SCHEDULED,
    VAV Sys 1 Avail,         !- Name
    AirSysAvailSched;        !- Schedule name

SYSTEM AVAILABILITY MANAGER:SCHEDULED,
    Dual Duct System 1 Schedule,  !- Name
    FanAndCoilAvailSched;    !- Schedule name

!-   ===========  ALL OBJECTS IN CLASS: SET POINT MANAGER:SCHEDULED ===========

SET POINT MANAGER:SCHEDULED,
    Supply Air Temp Manager, !- Name
    TEMP,                    !- Control variable
    Seasonal Reset Supply Air Temp Sch,  !- Schedule Name
    Supply Air Temp Nodes;   !- Name of the set point Node List

SET POINT MANAGER:SCHEDULED,
    Heating Coil Supply Air Temp Manager,  !- Name
    TEMP,                    !- Control variable
    Heating Coil Supply Air Temp Sch,  !- Schedule Name
    Heating Coil Supply Air Temp Nodes;  !- Name of the set point Node List


!-   ===========  ALL OBJECTS IN CLASS: SET POINT MANAGER:OUTSIDE AIR
===========

SET POINT MANAGER:OUTSIDE AIR,
    Supply Air Temp Manager 1,  !- Name
    TEMP,                    !- Control variable
    16.7,                    !- Set point at outside low {C}
    0.0,                     !- Outside low {C}
    12.8,                    !- Set point at outside high {C}
    32.8,                    !- Outside high {C}
    Supply Fan Inlet Temp Nodes;  !- Name of the set point Node List


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:SIMPLE ===========

CONTROLLER:SIMPLE,
! $$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$
    Main Cooling Coil Controller,  !- Name
    TEMP,                    !- Control variable
    Reverse,                 !- Action
    FLOW,                    !- Actuator variable
    Cooling Coil Outlet Node,!- Control_Node
    Cooling Coil Water Inlet Node,  !- Actuator_Node
    0.001,                   !- Controller Convergence Tolerance: delta temp
from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0.0;                     !- Min Actuated Flow {m3/s}

CONTROLLER:SIMPLE,
    Main Heating Coil Controller,  !- Name
    TEMP,                    !- Control variable
    Normal,                  !- Action
    FLOW,                    !- Actuator variable
    Heating Coil Outlet Node,!- Control_Node
    Heating Coil Water Inlet,!- Actuator_Node
    0.01,                    !- Controller Convergence Tolerance: delta temp
from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0.0;                     !- Min Actuated Flow {m3/s}


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:OUTSIDE AIR ===========

CONTROLLER:OUTSIDE AIR,
    OA Controler 1,          !- Name
    ECONOMIZER,              !- EconomizerChoice
    RETURN AIR TEMP LIMIT,   !- ReturnAirTempLimit
    NO RETURN AIR ENTHALPY LIMIT,  !- ReturnAirEnthalpyLimit
    NO LOCKOUT,              !- Lockout
    FIXED MINIMUM,           !- MinimumLimit
    Supply Fan Inlet Node,   !- Control_Node
    Outside Air Inlet Node 1,!- Actuated_Node
    autosize,                !- minimum outside air flow rate {m3/s}
    autosize,                !- maximum outside air flow rate {m3/s}
    19,                      !- temperature limit {C}
    4,                       !- temperature lower limit {C}
    3,                       !- enthalpy limit {J/kg}
    Relief Air Outlet Node 1,!- Relief_Air_Outlet_Node
    Return Fan Outlet Node;  !- Return_Air_Node

!-   ===========  ALL OBJECTS IN CLASS: ZONE SPLITTER ===========

ZONE SPLITTER,
    ZoneColdAirSupplySplitter,  !- Splitter Name
    Main Cold Air Inlet,     !- Inlet_Node
    Zone ABC3 Dual Duct Cold Inlet,  !- Outlet_Node_1
    Zone DEF3 Dual Duct Cold Inlet,  !- Outlet_Node_2
    Zone ABC2 Dual Duct Cold Inlet,  !- Outlet_Node_3
    Zone DEF2 Dual Duct Cold Inlet,  !- Outlet_Node_4
    Zone ABC1 Dual Duct Cold Inlet,  !- Outlet_Node_5
    Zone DEF1 Dual Duct Cold Inlet;  !- Outlet_Node_6

ZONE SPLITTER,
    ZoneHotAirSupplySplitter,!- Splitter Name
    Main Hot Air Inlet,      !- Inlet_Node
    Zone ABC3 Dual Duct Hot Inlet,  !- Outlet_Node_1
    Zone DEF3 Dual Duct Hot Inlet,  !- Outlet_Node_2
    Zone ABC2 Dual Duct Hot Inlet,  !- Outlet_Node_3
    Zone DEF2 Dual Duct Hot Inlet,  !- Outlet_Node_4
    Zone ABC1 Dual Duct Hot Inlet,  !- Outlet_Node_5
    Zone DEF1 Dual Duct Hot Inlet;  !- Outlet_Node_6


!-   ===========  ALL OBJECTS IN CLASS: ZONE MIXER ===========

ZONE MIXER,
    ZoneReturnAirMixer,      !- Mixer Name
    Return Air Mixer Outlet, !- Outlet_Node
    Zone ABC3 Outlet Node,   !- Inlet_Node_1
    Zone DEF3 Outlet Node,   !- Inlet_Node_2
    Zone ABC2 Outlet Node,   !- Inlet_Node_3
    Zone DEF2 Outlet Node,   !- Inlet_Node_4
    Zone ABC1 Outlet Node,   !- Inlet_Node_5
    Zone DEF1 Outlet Node;   !- Inlet_Node_6


!-   ===========  ALL OBJECTS IN CLASS: FAN:SIMPLE:CONSTVOLUME ===========

FAN:SIMPLE:ConstVolume,
    Supply Fan 1,            !- Fan Name
    FanAndCoilAvailSched,    !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600.0,                   !- Delta Pressure {Pa}
    autosize,                !- Max Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    1.0,                     !- Motor In Airstream Fraction
    Supply Fan Inlet Node,   !- Fan_Inlet_Node
    Supply Fan Outlet Node;  !- Fan_Outlet_Node

FAN:SIMPLE:ConstVolume,
    Return Fan 1,            !- Fan Name
    FanAndCoilAvailSched,    !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600.0,                   !- Delta Pressure {Pa}
    autosize,                !- Max Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    1.0,                     !- Motor In Airstream Fraction
    Return Air Mixer Outlet, !- Fan_Inlet_Node
    Return Fan Outlet Node;  !- Fan_Outlet_Node




__________________________________
Do you Yahoo!?
The New Yahoo! Shopping - with improved product search
http://shopping.yahoo.com
  ----------

NODE LIST,
    Supply Fan Inlet Temp Nodes,  !- Node List Name
    Supply Fan Inlet Node;   !- Node_ID_1
    
!-   ===========  ALL OBJECTS IN CLASS: BRANCH LIST ===========

BRANCH LIST,
    Dual Duct Air Loop Branches,  !- Branch List Name
    Air Loop Main Branch,    !- Branch Name 1
    Heating Coil Air Sys Branch,  !- Branch Name 2
    Cooling Coil Air Sys Branch,  !- Branch Name 3
    Return Air Loop Branch;  !- Branch Name 4

BRANCH LIST,
    Cooling Supply Side Branches,  !- Branch List Name
    CW Pump Branch,          !- Branch Name 1
    Big Chiller Branch,      !- Branch Name 2
    Supply Bypass Branch,    !- Branch Name 3
    Cooling Supply Outlet;   !- Branch Name 4

!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========

BRANCH,
    Air Loop Main Branch,    !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    OUTSIDE AIR SYSTEM,      !- Comp1 Type
    OA System 1,             !- Comp1 Name
    Return Fan Outlet Node,  !- Comp1 Inlet Node Name
    Supply Fan Inlet Node,   !- Comp1 Outlet Node Name
    PASSIVE,                 !- Comp1 Branch Control Type
    FAN:SIMPLE:ConstVolume,  !- Comp2 Type
    Supply Fan 1,            !- Comp2 Name
    Supply Fan Inlet Node,   !- Comp2 Inlet Node Name
    Supply Fan Outlet Node,  !- Comp2 Outlet Node Name
    PASSIVE;                 !- Comp2 Branch Control Type

BRANCH,
    Return Air Loop Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    FAN:SIMPLE:ConstVolume,  !- Comp1 Type
    Return Fan 1,            !- Comp1 Name
    Return Air Mixer Outlet, !- Comp1 Inlet Node Name
    Return Fan Outlet Node,  !- Comp1 Outlet Node Name
    PASSIVE;                 !- Comp1 Branch Control Type

BRANCH,
    Heating Coil Air Sys Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleHeating,!- Comp1 Type
    Main Heating Coil,       !- Comp1 Name
    Heating Coil Inlet Node, !- Comp1 Inlet Node Name
    Heating Coil Outlet Node,!- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type

BRANCH,
    Cooling Coil Air Sys Branch,  !- Branch Name
    autosize,                !- Maximum Branch Flow Rate {m3/s}
    COIL:Water:SimpleCooling,!- Comp1 Type
    Simple Cooling Coil,     !- Comp1 Name
    Cooling Coil Inlet Node, !- Comp1 Inlet Node Name
    Cooling Coil Outlet Node,!- Comp1 Outlet Node Name
    ACTIVE;                  !- Comp1 Branch Control Type



!-   ===========  ALL OBJECTS IN CLASS: AIR PRIMARY LOOP ===========

AIR PRIMARY LOOP,
    Main Dual Duct Air Loop, !- Primary Air Loop Name
    Dual Duct System 1 Controllers,  !- Name: Controller List
    Dual Duct System 1 Schedule List,  !- Name: System Availability Manager List
    autosize,                !- Primary air design volumetric flow rate {m3/s}
    Dual Duct Air Loop Branches,  !- Air Loop Branch List Name
    Dual Duct Connectors,    !- Air Loop Connector List Name
    Return Fan Outlet Node,  !- ReturnAir AirLoop Inlet Node
    Return Air Mixer Outlet, !- ZoneEquipGroup Outlet Node
    Zone Equipment Inlet Node List,  !- SupplyAirPath ZoneEquipGroup Inlet Nodes
    Air Loop Outlet Node List;  !- AirLoop Outlet Nodes


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER LIST ===========

CONTROLLER LIST,
    Dual Duct System 1 Controllers,  !- Name
    Controller:Simple,       !- Controller Type 1
    Main Cooling Coil Controller,  !- Controller Name 1
    Controller:Simple,       !- Controller Type 2
    Main Heating Coil Controller;  !- Controller Name 2

CONTROLLER LIST,
    OA System 1 Controller,  !- Name
    CONTROLLER:OUTSIDE AIR,  !- Controller Type 1
    OA Controler 1;          !- Controller Name 1

!-   ===========  ALL OBJECTS IN CLASS: AIR LOOP EQUIPMENT LIST ===========

AIR LOOP EQUIPMENT LIST,
    OA System 1 Equipment,   !- Name
    OUTSIDE AIR MIXER,       !- KEY--System Component 1
    OA Mixing Box 1;         !- Component Name 1


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR SYSTEM ===========

OUTSIDE AIR SYSTEM,
    OA System 1,             !- Name
    OA System 1 Controller,  !- Name: Controller List
    OA System 1 Equipment,   !- Name of an Air Loop Equipment List
    VAV Sys 1 Avail List;    !- Name of a System Availability Manager List


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR INLET NODE LIST ===========

OUTSIDE AIR INLET NODE LIST,
    OA Inlet Node 1;         !- 1st Node name or node list name


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE AIR MIXER ===========

OUTSIDE AIR MIXER,
    OA Mixing Box 1,         !- Name
    Supply Fan Inlet Node,   !- Mixed_Air_Node
    Outside Air Inlet Node 1,!- Outside_Air_Stream_Node
    Relief Air Outlet Node 1,!- Relief_Air_Stream_Node
    Return Fan Outlet Node;  !- Return_Air_Stream_Node

!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER LIST ===========

SYSTEM AVAILABILITY MANAGER LIST,
    VAV Sys 1 Avail List,    !- Name
    SYSTEM AVAILABILITY MANAGER:SCHEDULED,  !- System Availability Manager type 1
    VAV Sys 1 Avail;         !- System Availability Manager name 1

SYSTEM AVAILABILITY MANAGER LIST,
    Dual Duct System 1 Schedule List,  !- Name
    SYSTEM AVAILABILITY MANAGER:SCHEDULED,  !- System Availability Manager type 1
    Dual Duct System 1 Schedule;  !- System Availability Manager name 1


!-   ===========  ALL OBJECTS IN CLASS: SYSTEM AVAILABILITY MANAGER:SCHEDULED ===========

SYSTEM AVAILABILITY MANAGER:SCHEDULED,
    VAV Sys 1 Avail,         !- Name
    AirSysAvailSched;        !- Schedule name

SYSTEM AVAILABILITY MANAGER:SCHEDULED,
    Dual Duct System 1 Schedule,  !- Name
    FanAndCoilAvailSched;    !- Schedule name

!-   ===========  ALL OBJECTS IN CLASS: SET POINT MANAGER:SCHEDULED ===========

SET POINT MANAGER:SCHEDULED,
    Supply Air Temp Manager, !- Name
    TEMP,                    !- Control variable
    Seasonal Reset Supply Air Temp Sch,  !- Schedule Name
    Supply Air Temp Nodes;   !- Name of the set point Node List

SET POINT MANAGER:SCHEDULED,
    Heating Coil Supply Air Temp Manager,  !- Name
    TEMP,                    !- Control variable
    Heating Coil Supply Air Temp Sch,  !- Schedule Name
    Heating Coil Supply Air Temp Nodes;  !- Name of the set point Node List


!-   ===========  ALL OBJECTS IN CLASS: SET POINT MANAGER:OUTSIDE AIR ===========

SET POINT MANAGER:OUTSIDE AIR,
    Supply Air Temp Manager 1,  !- Name
    TEMP,                    !- Control variable
    16.7,                    !- Set point at outside low {C}
    0.0,                     !- Outside low {C}
    12.8,                    !- Set point at outside high {C}
    32.8,                    !- Outside high {C}
    Supply Fan Inlet Temp Nodes;  !- Name of the set point Node List


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:SIMPLE ===========

CONTROLLER:SIMPLE,
! $$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$$
    Main Cooling Coil Controller,  !- Name
    TEMP,                    !- Control variable
    Reverse,                 !- Action
    FLOW,                    !- Actuator variable
    Cooling Coil Outlet Node,!- Control_Node
    Cooling Coil Water Inlet Node,  !- Actuator_Node
    0.001,                   !- Controller Convergence Tolerance: delta temp from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0.0;                     !- Min Actuated Flow {m3/s}

CONTROLLER:SIMPLE,
    Main Heating Coil Controller,  !- Name
    TEMP,                    !- Control variable
    Normal,                  !- Action
    FLOW,                    !- Actuator variable
    Heating Coil Outlet Node,!- Control_Node
    Heating Coil Water Inlet,!- Actuator_Node
    0.01,                    !- Controller Convergence Tolerance: delta temp from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0.0;                     !- Min Actuated Flow {m3/s}


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:OUTSIDE AIR ===========

CONTROLLER:OUTSIDE AIR,
    OA Controler 1,          !- Name
    ECONOMIZER,              !- EconomizerChoice
    RETURN AIR TEMP LIMIT,   !- ReturnAirTempLimit
    NO RETURN AIR ENTHALPY LIMIT,  !- ReturnAirEnthalpyLimit
    NO LOCKOUT,              !- Lockout
    FIXED MINIMUM,           !- MinimumLimit
    Supply Fan Inlet Node,   !- Control_Node
    Outside Air Inlet Node 1,!- Actuated_Node
    autosize,                !- minimum outside air flow rate {m3/s}
    autosize,                !- maximum outside air flow rate {m3/s}
    19,                      !- temperature limit {C}
    4,                       !- temperature lower limit {C}
    3,                       !- enthalpy limit {J/kg}
    Relief Air Outlet Node 1,!- Relief_Air_Outlet_Node
    Return Fan Outlet Node;  !- Return_Air_Node

!-   ===========  ALL OBJECTS IN CLASS: ZONE SPLITTER ===========

ZONE SPLITTER,
    ZoneColdAirSupplySplitter,  !- Splitter Name
    Main Cold Air Inlet,     !- Inlet_Node
    Zone ABC3 Dual Duct Cold Inlet,  !- Outlet_Node_1
    Zone DEF3 Dual Duct Cold Inlet,  !- Outlet_Node_2
    Zone ABC2 Dual Duct Cold Inlet,  !- Outlet_Node_3
    Zone DEF2 Dual Duct Cold Inlet,  !- Outlet_Node_4
    Zone ABC1 Dual Duct Cold Inlet,  !- Outlet_Node_5
    Zone DEF1 Dual Duct Cold Inlet;  !- Outlet_Node_6

ZONE SPLITTER,
    ZoneHotAirSupplySplitter,!- Splitter Name
    Main Hot Air Inlet,      !- Inlet_Node
    Zone ABC3 Dual Duct Hot Inlet,  !- Outlet_Node_1
    Zone DEF3 Dual Duct Hot Inlet,  !- Outlet_Node_2
    Zone ABC2 Dual Duct Hot Inlet,  !- Outlet_Node_3
    Zone DEF2 Dual Duct Hot Inlet,  !- Outlet_Node_4
    Zone ABC1 Dual Duct Hot Inlet,  !- Outlet_Node_5
    Zone DEF1 Dual Duct Hot Inlet;  !- Outlet_Node_6


!-   ===========  ALL OBJECTS IN CLASS: ZONE MIXER ===========

ZONE MIXER,
    ZoneReturnAirMixer,      !- Mixer Name
    Return Air Mixer Outlet, !- Outlet_Node
    Zone ABC3 Outlet Node,   !- Inlet_Node_1
    Zone DEF3 Outlet Node,   !- Inlet_Node_2
    Zone ABC2 Outlet Node,   !- Inlet_Node_3
    Zone DEF2 Outlet Node,   !- Inlet_Node_4
    Zone ABC1 Outlet Node,   !- Inlet_Node_5
    Zone DEF1 Outlet Node;   !- Inlet_Node_6


!-   ===========  ALL OBJECTS IN CLASS: FAN:SIMPLE:CONSTVOLUME ===========

FAN:SIMPLE:ConstVolume,
    Supply Fan 1,            !- Fan Name
    FanAndCoilAvailSched,    !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600.0,                   !- Delta Pressure {Pa}
    autosize,                !- Max Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    1.0,                     !- Motor In Airstream Fraction
    Supply Fan Inlet Node,   !- Fan_Inlet_Node
    Supply Fan Outlet Node;  !- Fan_Outlet_Node

FAN:SIMPLE:ConstVolume,
    Return Fan 1,            !- Fan Name
    FanAndCoilAvailSched,    !- Available Schedule
    0.7,                     !- Fan Total Efficiency
    600.0,                   !- Delta Pressure {Pa}
    autosize,                !- Max Flow Rate {m3/s}
    0.9,                     !- Motor Efficiency
    1.0,                     !- Motor In Airstream Fraction
    Return Air Mixer Outlet, !- Fan_Inlet_Node
    Return Fan Outlet Node;  !- Fan_Outlet_Node



[Non-text portions of this message have been removed]


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/