Re: [EnergyPlus_Support] Shading control



To do this:

1. In MATERIAL:WINDOWBLIND set
    Slat angle = 105
2. In WINDOWSHADINGCONTROL set
    Shading Control Type = AlwaysOn
   Type of Slat Angle Control for Blinds = FixedSlatAngle

Note that "AlwaysOn" means that the blind will be in place day and night.

Fred Winkelmann

dameco@xxxxxxxxx wrote:

> I have some problem with shading control:
> I want a control "always on" at night, instead during the day I need
> to have a control on the angle of blind slat. Blind is exterior and
> the angle that I want is 105° respect to the orizontal. I need this
> control to massimize the solar gain in winter.
> How I can to do?
> Thanks Ale.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
>
>
>
>
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
>  http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to:
>  http://docs.yahoo.com/info/terms/


To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Yahoo! Groups Links

To visit your group on the web, go to:
 http://groups.yahoo.com/group/EnergyPlus_Support/

To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

Your use of Yahoo! Groups is subject to:
 http://docs.yahoo.com/info/terms/