[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] corridors



You have two options.  One is to use MIXING or CROSS MIXING to exchange air 
between the office and corridor zones.  You must determine an appropriate flow 
rate and schedule.  The other option is to set up a COMIS network to model the 
infiltration and mixing flows induced by the wind.  I would suggest the first 
option unless you have need of a detailed natural ventilation model.

Mike


On 21 Jun 2004, at 1:42, teklay weldeabzgi wrote:

>  i am simulating a two story office building with a corridor in each floor. the
>  corridor is not conditioned and it separates the office rooms. so how do i
>  consider this space? i am trying to treat as one zone but i can't understand
>  how to take to account the infilatration b/n the corridor and the office rooms.
>  another difficulty is the door of the corridor is opened for almost all the
>  office hours and this seems the air temperature of the inside corridor is the
>  same as the outside environmet but i think it will be less than that due to
>  infiltration from the conditioned office rooms. 
> so how do i consider these  all things in my simulation.
> thanks
> tek  
> 
> 
> ---------------------------------
> Do you Yahoo!?
> New and Improved Yahoo! Mail - 100MB free storage!
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/