[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Controller error messages



At 01:48 PM 7/14/2004, sm278424 wrote:

>I'm having difficulty finding a solution to the following messages:
>
>
>
>    ** Warning ** The design coil load is zero for
>COIL:Water:SimpleHeating AHU HEATING COIL 1
>    **   ~~~   ** The autosize value for max water flow rate is zero
>    **   ~~~   ** To change this, input a value for UA, change the
>heating design day, or lower
>    **   ~~~   **   the system heating design supply air temperature
>
>    ** Severe  ** Missing temperature setpoint for economizer
>controller OA CONTROLLER 1:
>
>    ** Severe  ** Node Referenced (in Controller)=MIXED AIR NODE 1
>    **   ~~~   **   use a Set Point Manager to establish a setpoint at
>the mixed air node.

Not so sure about above error messages but this one

>    ** Warning ** Did not find "Mixed Air Node 1" in list of Sections

is due to the two lines in your included input that end in ";"

>SET POINT MANAGER:MIXED AIR,
>     Mixed Air Temp Manager 1,
>     TEMP,
>     CC Air Outlet Node 1,    ! reference node
>     Mixed Air Node 1,        !- Fan_Inlet_Node
>     CC Air Outlet Node 1;     !- Fan_Outlet_Node
>     Mixed Air Node 1;        !- Name of the set point Node or Node List
>

Change to:
SET POINT MANAGER:MIXED AIR,
     Mixed Air Temp Manager 1,
     TEMP,
     CC Air Outlet Node 1,    ! reference node
     Mixed Air Node 1,        !- Fan_Inlet_Node
     CC Air Outlet Node 1,     !- Fan_Outlet_Node
     Mixed Air Node 1;        !- Name of the set point Node or Node List

and see if that helps.


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/