[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] cooling load



These will be equal when the PURCHASED AIR "Outside air flow rate" is zero (see 
PurchAir example file).  If the outside air flow rate is greater than zero, 
then "Zone/Sys Sensible Cooling Energy" represents the cooling delivered to the 
zone, and the "Purchased Air Sensible Cooling Energy" is the cooling required 
to condition the mixed air to the specified supply condition.  

Mike


On 22 Aug 2004, at 23:51, teklay Weldeabzgi wrote:

> 
>  hello everybody
> i can't understand Purchased Air Sensible Cooling
> Energy[J] is different from Zone/Sys Sensible Cooling
> Energy[J]. 
> 
> 
> 
> __________________________________
> Do you Yahoo!?
> Read only the mail you want - Yahoo! Mail SpamGuard.
> http://promotions.yahoo.com/new_mail 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/