[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] about MTF




Dear:
 
The file that I have uploded named "W only enve MTF" had only envelope, no infirltration and others. Then the latent load should be the permeating from building materials. that value is too large! Why?

Edward Lyon <eglyon@xxxxxxx> wrote:
The latent load that permeats building materials is small.  The latent
load that is carried by air penetrating the building envelope is large. 
If you have normal infiltration of say .35 air changes, the
recommendation for a small house, you may have significant latent load
depending on your climate.

Ned Lyon

Senior Project Manager
Simpson Gumpertz & Heger Inc.

41 Seyon Street
Building #1, Suite 500
Waltham, MA  02453

Phone:  781-907-9000
Fax:  781-907-9009

>>> lizhenghdf@xxxxxxxxxxxx 08/27/04 8:00 AM >>>



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.



Yahoo! Groups SponsorADVERTISEMENT


---------------------------------
Yahoo! Groups Links

   To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
  
   To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
  
   Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 



---------------------------------
薛凱琪聲色圖案、語音聊天、寬頻Webcam等多項功能
全新 Yahoo! Messenger
http://messenger.yahoo.com.hk

[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/