[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Modeling Art Galleries




I would be cautious about using a displacement design for an art
gallery.  I'm reasonably sure that you can get good energy performance
data from an Energy+ model, but that may not translate into a successful
design.  If the museum is cold climate, you are likely to face
condensation problems with exterior walls that are not predictable with
Energy+.  Art hung on exterior walls is also problematic since the art
will "see" the wall thermal loads and the displacement ventilation will
not sweep the exterior walls to maintain temperature.  If you use
Energy+ for overall energy performance modeling, you should use other
programs for more detailed analysis.  You probably need CFD runs for
more detailed interior airflow and surface temperature analysis as well
as a more detailed thermal analysis of potential thermal bridges in the
wall assembly. 

Ned Lyon

Senior Project Manager
Simpson Gumpertz & Heger Inc.

41 Seyon Street
Building #1, Suite 500
Waltham, MA  02453

Phone:  781-907-9000
Fax:  781-907-9009


>>> dan_grunbaum@xxxxxxxxx 11/21/2004 5:54:15 AM >>>
Hi there,

Is EnergyPlus suitable to model art galleries using displacement units?
Given that a high degree of accuracy is required how reliable would the
results be ?

Thanks

Dan



---------------------------------
Find local movie times and trailers on Yahoo! Movies.


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov 

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ 

Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.



Yahoo! Groups Sponsor 
Get unlimited calls to
U.S./Canada
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/ 
  To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/