Re: [EnergyPlus_Support] whether the first component on cooling supply loop must be a pump or not?




EnergyPlus only allows one pump per plant/condenser loop, and it must be the 
first component on the supply side of the loop.  By using a variable speed pump 
with a linear part load curve with no bypass, you can come fairly close to 
approximating the energy use of three separate pumps that operate with each 
chiller.

Mike


On 14 Dec 2004, at 2:41, zyyh9819 wrote:

> 
> 
> hi£¬
> 
>    I met a fatal error in my simulation. The following is the fatal 
> error:
> 
>  **  Fatal  ** The following pump is not the first component on its 
> loop: CW FIRST PUMP_1
> 
>   There are three chillers and three pumps on cooling supply loop of 
> my idf file, so the first component in cooling supply loop is a 
> pipe, following is a splitter. 
>   The question is whether the first component on cooling supply loop 
> must be a pump or not?
>   I have upload my idf file(sunflower.rar). please help me to check 
> it.I will very appreciate it !
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$4.98 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/Q7_YsB/neXJAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/