Re: [EnergyPlus_Support] A Warning about Simple Heating Coil




These warnings come from the controller for the reheat coil in the VAV unit and 
indicate that the controller was not able to match the zone load within the 
specified convergence tolerance .  Using a larger value in the "convergence 
tolerance" field in the SINGLE DUCT:VAV:REHEAT object can get rid of these 
warnings, but it may cause other iteration problems elsewhere in the 
simulation.  If the zone temperature is maintained close to the desired 
setpoint, then you can ignore these warnings.

Mike


On 6 Jan 2005, at 10:51, zhen tian wrote:

> 
> Hi, All:
> 
> I got 13 warnings like the following during my simulation of 12 zones with 3 VAV
> systems.  Each zone has reheat coil. "Warning ** ControlCompOutput: Maximum
> iterations exceeded for COIL:WATER:SIMPLEHEATING".
> 
> Could somebody tell me what may be the reason for causing these warnings and how
> can get rid of these.  Actually, when I used 1 step/hour, I did not get these
> warnings, but when I changed to 4 steps/ hour in the simulation, these warnings
> appeared.
> 
> Thanks a lot for your help.
> 
> Regards,
> 
> Zhen
> 
> 
> 
> ---------------------------------
> Do you Yahoo!?
>  Yahoo! Mail - Easier than ever with enhanced search. Learn more.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/