[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: EIR Chiller Performance Curve Fitting



Dear Sam

     I am wondering whether I can get a internship or a part-time job from you. I will 
graduate in Mar next year.

                                                                                                       charlie 




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee <samwslee@y...> wrote:
> Hi Charli,
>  
> Still in planning, it would be one of the famous consultant company.
>  
> SAMLEE 
> 
> applezealot <applezealot@y...> »¡¡G
> Dear Sam
> 
>       I am studying in developing an absorption chiller which can use the recovery heat 
from 
> chillers and engines. I reseach the chiller modules for the purpose. What will you do in 
> shanghai? And who will you work for?
> 
>                                                                                       charlie
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee <samwslee@y...> wrote:
> > Hi,
> >  
> > Which course or module that you are studying? May be I have a chance to work at 
> Shanghai at the end of this year.  
> >  
> > SAM
> > 
> > applezealot <applezealot@y...> »¡?G
> > Dear Sam
> > 
> >      I am a gradute student in Shanghai Jiaotong University. If you 
> > have the problem of reading Chinese,it will be alright that we could 
> > still discuss in English. Thank you very much for your patient and 
> > help. We start using the software about half a year. And I need to 
> > use E+ to complete my thesis. So I won't hesitate to ask you for your 
> > help if I get into trouble with E+
> >      Best wishes
> >      See you
> >                                                         charlie
> >      
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee 
> > <samwslee@y...> wrote:
> > > Hi,
> > >  
> > > Ok, but I type Chinese Word very slowly and I worry about that I 
> > can see the simplified words in my computer. May be you can try it!
> > >  
> > > I live in Hong Kong and work at Government Department, so I have 
> > chance to use EnergyPlus to simulate various Government property in 
> > Hong Kong. Since I have successfully simulate two nos of the 
> > Government Buildings, those simulation results can reflect the actual 
> > energy use.
> > >  
> > > If you have any problem, please don't hesitate to discuss with me.
> > >  
> > > **Which university you study?
> > >  
> > > SAMLEE 
> > > 
> > > applezealot <applezealot@y...> »¡?G
> > > Dear Sam
> > >      Thank you very much for your help. And nice meeting you 
> > through 
> > > the internet. I am a graduate student in shanghai studying E+ for 
> > > about 4 months. Are you a chinese too? Maybe we speak our lanaguage 
> > > to discuss the issues about the software.
> > >      Is that OK for you?
> > > 
> > >                                                  charlie
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee 
> > > <samwslee@y...> wrote:
> > > > Hi Charlie,
> > > >  
> > > > As compare between predicted simulation result and the actual 
> > > energy use, the error is within 5%. So it is realistic.
> > > >  
> > > > SAMLEE
> > > > 
> > > > applezealot <applezealot@y...> »¡?G
> > > > Hi Sam
> > > >    I gott you. But I am not sure that the third curve you defined 
> > > is 
> > > > able to simulate the chiller performance. Since you have done 
> > some 
> > > > work on the chiller module, does the results show the correctness?
> > > >    Thank you very much for your help
> > > > 
> > > >                                                     charlie
> > > > 
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee 
> > > > <samwslee@y...> wrote:
> > > > > Hi Charlie,
> > > > >  
> > > > > As you know 1) the PRL is equal to the rated cooling load 
> > divided 
> > > > by the available cooling load. e.g. from the manufacture, tha 
> > > > standard rating for the specific leaving chilled water 
> > temperature 
> > > > (6.7oC) and the entering air temperature (35oC). 
> > > > > 2) the value ChillerEIRFPLR (Y) is EIRavailable / (EIRdesign x 
> > > > PRL).  You can refer to the EngineeringDoc P.338.
> > > > >  
> > > > > SAMLEE
> > > > > 
> > > > > applezealot <applezealot@y...> »¡?G
> > > > > Dear sam
> > > > > 
> > > > >       I check your excel file. I have some question about your 
> > > > > calculation:
> > > > >   1. You used (Qr/Qa) as PLR and (Pa/Pr) as EIR output ratio 
> > for 
> > > > the 
> > > > > third.I get confused about these settings. Could you please 
> > tell 
> > > > me 
> > > > > why you choose these parameters? P.S. Pa,Pr,Qa,Qr are power 
> > > > > available, power rated, capacity available and capacity rated.
> > > > >   2. And I look into the curve fitting results in sheet1 of 
> > your 
> > > > > file. Is it related to our discussion?  I can not understand 
> > the 
> > > > > purpose of this sheet. Please explain it for me.
> > > > > 
> > > > >        Thank you in advance
> > > > >                                                     charlie
> > > > > 
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee 
> > > > > <samwslee@y...> wrote:
> > > > > > Hi,
> > > > > >  
> > > > > > Please go here 
> > > > > 
> > > > 
> > > 
> > http://groups.yahoo.com/group/EnergyPlus_Support/Files/Problem_Submit
> > > > > tals/Input Problem/Fit curve biquadratic d.xls 
> > > > > > 
> > > > > > It seems to be corrected and solved
> > > > > > 
> > > > > > SAMLEE
> > > > > > 
> > > > > > 
> > > > > > donbshireyiii <shirey@f...> ¼¶?g:
> > > > > > Charlie and SAMLEE,
> > > > > > 
> > > > > > In the spreadsheet you are using, it looks like EIR as a 
> > > function
> > > > > > of PLR is not being properly calculated.
> > > > > > 
> > > > > > The spreadsheet seems to be using available capacity at the 
> > > > current
> > > > > > operating conditions divided by the design (rated) capacity 
> > of 
> > > > the
> > > > > > chiller.  This is not correct.... is should be just as the
> > > > > > input/output reference says... PLR = (cooling load) divided by
> > > > > > (available capacity at the current operating conditions).
> > > > > > 
> > > > > > Don 
> > > > > > 
> > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, wing sun lee
> > > > > > <samwslee@y...> wrote:
> > > > > > > Hi Charlie,
> > > > > > >  
> > > > > > > I just use your advice that the PRL shoudl equal to the 
> > ratio 
> > > > of
> > > > > > cooling load to the available capacity. 
> > > > > > > Please see my attached file at
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/F
> > > > > > iles/Problem_Submittals/Input
> > > > > > Problem/Fit curve biquadratic b.xls 
> > > > > > >  
> > > > > > > SAMLEE
> > > > > > > 
> > > > > > > energypluser <energypluser@y...> ¼¶?g:
> > > > > > > Dear Mike,
> > > > > > > 
> > > > > > >      I wanna simulate a electric chiller with the EIR 
> > module. 
> > > > > And I 
> > > > > > > found that you give a EXCEL example for the curve fitting. 
> > > But 
> > > > I
> > > > > > think 
> > > > > > > the third curve in your example file may not be correct. 
> > > > > > >      According to the input/output reference, the third 
> > curve 
> > > > is
> > > > > > the 
> > > > > > > EIR output ratio in function of Part Load Ratio. The PLR
> > > > > > calculation in 
> > > > > > > your file is the ratio of the available capacity to the 
> > > > nominal 
> > > > > > > capacity.  In my opinion, PLR should equal to the ratio of 
> > the
> > > > > > cooling 
> > > > > > > load to the available capacity. Am I right?
> > > > > > >       If I am right, could you please tell me how to obtain 
> > > the
> > > > > > third 
> > > > > > > curve for my simulation based on the manufacturer catalog.
> > > > > > >       Thank you in adavance
> > > > > > > 
> > > > > > >                                                             
> > > > > charlie 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > The primary EnergyPlus web site is found at:
> > > > > > http://www.energyplus.gov
> > > > > > 
> > > > > > The group web site is:
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > > 
> > > > > > Attachments are not allowed -- please post any files to the 
> > > > > appropriate folder in the Files area of the Support Web Site.
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > ---------------------------------
> > > > > > Yahoo! Groups Links
> > > > > > 
> > > > > >    To visit your group on the web, go to:
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > >   
> > > > > >    To unsubscribe from this group, send an email to:
> > > > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > > >   
> > > > > >    Your use of Yahoo! Groups is subject to the Yahoo! Terms 
> > of 
> > > > > Service. 
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > ---------------------------------
> > > > > > ?Q?Y?¦¬??s email ?q??H
> > > > > > ?U¸ü Yahoo! Messenger
> > > > > > http://messenger.yahoo.com.hk
> > > > > > 
> > > > > > [Non-text portions of this message have been removed]
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > The primary EnergyPlus web site is found at:
> > > > > http://www.energyplus.gov
> > > > > 
> > > > > The group web site is:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > 
> > > > > Attachments are not allowed -- please post any files to the 
> > > > appropriate folder in the Files area of the Support Web Site.
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > ---------------------------------
> > > > > Yahoo! Groups Links
> > > > > 
> > > > >    To visit your group on the web, go to:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > >   
> > > > >    To unsubscribe from this group, send an email to:
> > > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > >   
> > > > >    Your use of Yahoo! Groups is subject to the Yahoo! Terms of 
> > > > Service. 
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > ---------------------------------
> > > > > ?Q?Y?¦¬??s email ?q??H
> > > > > ?U¸ü Yahoo! Messenger
> > > > > http://messenger.yahoo.com.hk
> > > > > 
> > > > > [Non-text portions of this message have been removed]
> > > > 
> > > > 
> > > > 
> > > > 
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > > 
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > 
> > > > Attachments are not allowed -- please post any files to the 
> > > appropriate folder in the Files area of the Support Web Site.
> > > > 
> > > > 
> > > > 
> > > > 
> > > > ---------------------------------
> > > > Yahoo! Groups Links
> > > > 
> > > >    To visit your group on the web, go to:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >   
> > > >    To unsubscribe from this group, send an email to:
> > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >   
> > > >    Your use of Yahoo! Groups is subject to the Yahoo! Terms of 
> > > Service. 
> > > > 
> > > > 
> > > > 
> > > > ---------------------------------
> > > > ?Q?Y?¦¬??s email ?q??H
> > > > ?U¸ü Yahoo! Messenger
> > > > http://messenger.yahoo.com.hk
> > > > 
> > > > [Non-text portions of this message have been removed]
> > > 
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the 
> > appropriate folder in the Files area of the Support Web Site.
> > > 
> > > 
> > > 
> > > 
> > > ---------------------------------
> > > Yahoo! Groups Links
> > > 
> > >    To visit your group on the web, go to:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >   
> > >    To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >   
> > >    Your use of Yahoo! Groups is subject to the Yahoo! Terms of 
> > Service. 
> > > 
> > > 
> > > 
> > > ---------------------------------
> > > ?Q?Y?¦¬??s email ?q??H
> > > ?U¸ü Yahoo! Messenger
> > > http://messenger.yahoo.com.hk
> > > 
> > > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder in the 
> Files area of the Support Web Site.
> > 
> > 
> > 
> > 
> > ---------------------------------
> > Yahoo! Groups Links
> > 
> >    To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >   
> >    To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >   
> >    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> > 
> > 
> > 
> > ---------------------------------
> > ?Q?Y?¦¬??s email ?q??H
> > ?U¸ü Yahoo! Messenger
> > http://messenger.yahoo.com.hk
> > 
> > [Non-text portions of this message have been removed]
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the 
Files area of the Support Web Site.
> 
> 
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>   
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>   
>    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> 
> ---------------------------------
> ·Q§Y®É¦¬¨ì·s email ³qª¾¡H
> ¤U¸ü Yahoo! Messenger
> http://messenger.yahoo.com.hk
> 
> [Non-text portions of this message have been removed]




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/