Re: [EnergyPlus_Support] VRV with heat recovery system ,outside condenser water cooled



EnergyPlus does not have a VRV system model.  The best approximation for what 
you describe would be to use UNITARYSYSTEM:HEATPUMP:WATERTOAIR.  Example file 
HeatPumpWaterToAir uses this system with a ground heat exchanger, but it can 
work with any type of equipment on the water side.

Mike


On 27 May 2005, at 8:16, glasses12300202 wrote:

> Dear all:
> 
>       Can VRV with heat recovery system uses EP to simulate,and how to 
> input the .idf file?
> 
>       My system is VRV(variable refrigerant volume) with heat recovery 
> system ,of which  the outside heat exchanger(condenser)  is cooled by 
> water in summer.    
> 
>       It is the refrigerant which flows in the conduit  .So I want to 
> know how to input the .idf file  ? Is there any example about VRV 
> system?   
> 
> 
>            Thanks for your return
> 
>                                  Donovan
>                                 2005/5/27
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/