[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] comis network error



As it says in the error message, there must be at least one external node.  Add 
a small exterior crack in one of the zones.  Also, be careful with internal 
doors and windows.  For heat transfer there must be two adjacent surfaces, one 
in each zone, but COMIS only needs one opening between the two zone, not two.

Mike


On 10 Jun 2005, at 0:02, ogocer@xxxxxxxxxxxxxx wrote:

> 
> Dear all,
> i have simulated two story building. In front of it there is a two story
> height zone. and i defined comis air flow between these three zones
> without specifing any active system. it gave an error as in below. Because
> it is a rectangular building i didn't specify external nodes. i defined
> the openings on adjacent surface as comis openings (these are windows and
> doors) how can i solve this problem. thanks alot
> ozgur gocer
> 
> 
> 
> NETWORK ERROR
>   &-NET-ZONe contains  3  zones.
>   At least one of the zones should be connected to a known pressure.
>   Two kinds of known pressures exist:
>    - external nodes. These have a negative number in &-NET-LINks
>    - special pressures. These have a form like nn.nPa (nn.n=a REAL number)
>   You have to add such a link to the network.
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/