[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: validation of extensive coefficients use



These are all normalized.  I am not aware of any EnergyPlus HVAC equipment 
curves that are not normalized.  

Mike


On 12 Oct 2005, at 1:42, deserteagle_zhou wrote:

> Thank you,Brent/(Fred), for your elaborated explaination. So can I 
> assume that the "normalization" means a ratio of a real-condition 
> parameter to a rated-point one? Then how about curves of Electric 
> Chiller, WindAC,Direct-fired absorption Chiller? Are they called 
> normalized curves?
> 
> John
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent" 
> <brent_griffith@n...> wrote:
> >
> > John, 
> >  
> > Keep in mind that there are at least two possible "policies" for 
> curve-fits.  One option is to use curves that are normalized with 
> respect to capacity (or efficiency) at a single operating point.  
> The other is to use curves that directly fit the capacity/efficiency 
> data without normalization.   It is not unreasonable practice to use 
> normalized curves for components that have a different nominal 
> capacity or efficiency than the one used to produce the curves.  
> Clearly it is better to use performance curves that apply to the 
> unit being modeled, but this isn't always practical.  On the other 
> hand, direct performance curves (that aren't normalized) are 
> basically limited to the original unit and cannot be used to model 
> components with a different size or nominal performance.  
> >  
> > Developers have different opinions on which is the best way to 
> go.  The normalized-curve group want curves to be more general so 
> that one can easily adjust equipment capacities when doing a 
> simulation study.  The direct-curve group are more leary of the 
> pitfalls of abusing curves and want to force the user to use curves 
> that match the component.  I am not sure if it is true across the 
> board, but curves tend to be of the normalized type in EnergyPlus.  
> So it is not blatently wrong to reuse such curves for different 
> capacities.  However, do not assume that the example files that ship 
> with EnergyPlus represent best modeling practice. It is better to 
> think of them as test and demonstration files.       
> >  
> > Brent 
> > 
> >  -----Original Message-----
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of 
> deserteagle_zhou
> > Sent: Tuesday, October 11, 2005 4:13 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: [EnergyPlus_Support] validation of extensive coefficients 
> use
> > 
> > 
> > 
> > Hi,there,
> > 
> > Components, i.e., chiller, fan, etc, are defined according to a 
> > performance curve-fit policy. Curves, however, often have 
> something to 
> > do with the real working conditions and an equipment capacity. I 
> think 
> > users are not supposed to use directly the same coefficients as 
> before 
> > after the equipment capacity has been changed. That means we 'd 
> better 
> > not use directly the curves and parameters in E+ example files 
> directly 
> > unless we cannot get the data from the equipment producer.
> > Is this understanding right or not?
> > 
> > Another question is whether the object SINGLE DUCT:VAV REHEAT can 
> deal 
> > with heating condition alone in a zone without a company heating 
> device 
> > (such as a baseboard heater), especially in a cold area? 
> > 
> > Thank you. 
> > John
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
> and press the "search" button.
> > 
> > 
> > 
> > 
> >   _____  
> > 
> > YAHOO! GROUPS LINKS 
> > 
> > 
> > 	
> > *	 Visit your group " EnergyPlus_Support 
> <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
> >   
> > 
> > *	 To unsubscribe from this group, send an email to:
> >   EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
> subject=Unsubscribe> 
> >   
> > 
> > *	 Your use of Yahoo! Groups is subject to the Yahoo! Terms 
> of Service <http://docs.yahoo.com/info/terms/> . 
> > 
> > 
> >   _____  
> > 
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> >
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/