[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Cooling Tower: wet or dry cooling function



You can have indirect-contact (or closed-circuit) evaporative cooling 
towers that are "wet" towers.... see 2004 ASHRAE Handbook -- HVAC 
Systems and Equipment, Chapter 36, Figure 4.

Don Shirey wrote:

> See the discussion in the EnergyPlus Engineering Reference document for
> this object (search for Cooling Tower:Single Speed).
>
> It is modeling a wet tower, not a dry cooling tower.
>
>
> patrik_789 wrote:
>
> > Dear Sankar,
> >
> > in addition to the previously discussed problems, there are further
> > questions about the possibilities for the simulation of specific
> > systems and control / coupling modes for plant and condenser loops
> > and their components.
> > As you have seen, we use a cooling tower single speed in the first
> > condenser loop. The question is, if this kind of cooling tower (and
> > therefore all the cooling towers modeled in energy plus) is a wet
> > cooling tower or only a dry cooling tower with an integrated fan for
> > a better convection.
> > We are not sure about the functionality of this object, because
> > there are a lot of references to the wet bulb temperature in the
> > input output documentation: for the condenser loop temperature set
> > point mode and for the cooling tower wet bulb temperature difference
> > based operation.
> > But the definition of the cooling tower in the input output
> > documentation is: close circuit cooling tower, thus it can't be a
> > wet cooling tower.
> > If the cooling tower in energy plus is indeed a dry cooling tower,
> > how could we simulate a wet cooling tower?
> > Furthermore our real cooling tower can be switched between wet and
> > dry cooling function.
> > During the winter, when the outside temperatures are below 6 °C, the
> > cooling tower operates in a closed circuit modus with an operating
> > fan.
> > How could we implement/ simulate such a system/ case?
> > We would appreciate if you could point us in the right direction
> > towards the solution of this problem.
> > Best regards,
> >
> > Patrik





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/