[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Problems with coil:water:cooling in a unit ventilator



Dear all,
currently I'm modelling a server-room with high electric load (up to 
700W/m2). For zone cooling I'm using a UnitVentilator. Actually there 
are 4 cooling elements in the room. 

One element is specified as:
  Air-Temperature-in: 24 °C
  Air-Temperature-out: 14.2 °C
  Air-volumn flow rate: 6.11 m3/s
  Water-Temperature-in: 12 °C
  Water-Temperature-out:18 °C
  Water-volumn flow rate: 0.0029 m3/s
  Total cooling power: 73kW

The electric load in the zone is about 130kW. The 4 cooling elements 
have a total cooling power of ~292kW which is more then twice the 
internal load. So if the unit ventilator works correctly the zone 
should be exact on the zone setpoint temperature. 

When I use a coil:water:cooling in the unit ventilator and specify the 
input values as mentioned above (except the flow-rates have been 
multiplied with 4) the zone setpoint temperatures cannot be achieved!
Everything else seems to be OK: no errors, no warnings, correct air 
flow rate, correct water flow rate, correct water inlet temperature,.
.. (same result in E+ v1.2.2 and v1.2.3).

I've now manually calculated the UA value for my cooling element, 
changed the cooling coil to a coil:water:simplecooling object, used 
this UA value (93870 W/K for 4 elements) and the model will give the 
expected result. 

Are there any know issues using the UnitVentilator with a coil:water:
cooling?

Christian

PS: I will upload the idf file: unitVentilatorCoolingCoilProblem.zip





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/