[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Solar Array with Boiler for DHW



I'm going to try and send this again as the 'Rish Text Editor (Beta) 
made a mess of my last attempt...

I've been looking at that example?

On page 821 of the input/output reference document it says?

"In order to realize energy savings with a solar heating system, it 
is necessary to use the
WATER HEATER:STRATIFIED object for thermal storage."

To which water heater is this referring to?

I'm trying to emulate a system that uses 6 solar collectors that 
provide heating for DHW (similar to the example you highlighted). 
The water is initially heated in a vessel @40oC. When the solar 
collector does not provide enough heat to heat the water, extra 
heating is provided from a separate boiler circuit which also 
provides for other disparate systems. This water is then fed into 
another water heater which heats the DHW to a final temp of 60oC. 
Does anyone have any ideas how I might set up a similar system in 
E+. 

I would like some advice on how good/bad/awful my proposed is...

Approach (This is only possible if I can make the water heaters do 
nothing and impose a control whereby the full load is picked up by 
the water heater source. Is that possible?)

Solar Collector -> (temp pickup +) Heat Exchanger #1 ->  Water 
Heater #1 @40oC

Boiler -> splitter {  
                   (split 1)|-> Heat Exchanger #1 
  
	           (split 2)|-> Water Heater #2 @ 60oC -> DHW



?	I would set the Heat Exchanger #1's efficiency to values 
that make it similar to the efficiency of the water heater to boiler 
circuit setup. This should emulate a twin source for the water 
heater.

Does anyone have any thoughts?

Kind regards

-Elmer



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ellis, Peter" 
<peter_ellis@n...> wrote:
>
>  
> Hello Elmer,
>  
> The example file "SolarCollectorFlatPlateWater.idf" illustrates a 
solar hot water system with DHW load, solar collectors, and storage 
tank (WATER HEATER:MIXED).  You can connect a boiler, or another 
auxiliary WATER HEATER:MIXED (perhaps configured as instantaneous 
water heater), in series with the storage tank.
>  
> P
>  
>  
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Elmer 
Morrissey
> Sent: Thursday, January 05, 2006 12:31 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Solar Array with Boiler for DHW
> 
> 
> Hello all,
> 
> I am attempting a simulation of the system that provides hot water 
for 
> a building. 
> 
> System:
> A solar array and a gas fired boiler combine to provide the DHW 
load. 
> The solar array provides as much as it can and the rest of the 
load is 
> picked up by the boiler. Can anyone suggest how I can emulate this 
> kind of system or provide a similar example circuit? Is there some 
> form of object in E+ which acts as a buffer vessel for HW and can 
be 
> heated using two disparate loops?
> 
> Kind regards
> 
> -Elmer
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the "search" button.
> 
> 
> 
> 
>   _____  
> 
> YAHOO! GROUPS LINKS 
> 
> 
> 	
> *	 Visit your group " EnergyPlus_Support 
<http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
>   
> 
> *	 To unsubscribe from this group, send an email to:
>   EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
subject=Unsubscribe> 
>   
> 
> *	 Your use of Yahoo! Groups is subject to the Yahoo! Terms of 
Service <http://docs.yahoo.com/info/terms/> . 
> 
> 
>   _____  
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
>






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/