[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] maximum supply air temperature



Thanks,

I could already decrease the temperatures by increasing the minimum flow
rate, but I was just wondering if there is a better way.

Friedl

On 5/17/06, fred buhl <wfbuhl@xxxxxxx> wrote:
>
> Friedl: that is an excellent question. EnergyPlus does not control the
> reheat coils to
> an exit air temperature - the coils are controlled to meet the load, and
> the temperature is
> whatever results. This isn't a particularly good situation, but it is
> the way things are done now.
> You could mitigate your situation by decreasing the max hot water
> flowrate, or lowering the
> hot water supply temperature, or increasing the minimum air flow rate.
>
> Fred Buhl
>
>
> friedl decock wrote:
>
> >Hi,
> >
> >I'm trying to simulate a VAV-system but I'm not able to control the
> maximum
> >air supply temperature in the zone.
> >In the winter the supply air temperature exceeds sometimes 40 degrees
> while
> >the air flow rate is always the minimum value that is allowed.
> >
> >Does anyone know how to control the max temperature of the supply air in
> a
> >zone (after the reheat coil).
> >
> >Friedl
> >
> >
> >[Non-text portions of this message have been removed]
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
> the "search" button.
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>  The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
> the "search" button.
>
>
>
>  ------------------------------
> YAHOO! GROUPS LINKS
>
>
>    -  Visit your group "EnergyPlus_Support<http://groups.yahoo.com/group/EnergyPlus_Support>"
>    on the web.
>
>    -  To unsubscribe from this group, send an email to:
>     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx<EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
>    -  Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>    Service <http://docs.yahoo.com/info/terms/>.
>
>
>  ------------------------------
>


[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get to your groups with one click. Know instantly when new email arrives
http://us.click.yahoo.com/.7bhrC/MGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/