Regarding the bypass air reporting.  Everything looks OK here.  An explanation 
from the heat exchanger expert:

"The HeatExchanger:Air To Air:Generic object appears to be working 
correctly in the example file. For the rotary HX (example file as is), 
the air is not bypassed, the wheels rotational speed is varied to 
maintain an exhaust air outlet temperature equal to the threshold 
temperature for the time the HX is in defrost. The exhaust/supply air 
temperatures are averages over the time step so the user will not see 
the threshold temperature at the exhaust outlet node, its the average 
exhaust outlet temperature (will be lower than the threshold temperature 
if defrost fraction is less than 1). For the plate heat exchanger the 
supply air is bypassed (and verified in the example file when Heat 
Exchanger Type is changed to plate). Outlet temperatures are again the 
average over the time step."

Mike


On 14 Jun 2006 at 21:46, Michael J. Witte wrote:

> The drawing error may be a problem with hvac-diagram rather than the ERV model
> -
>  will look into it.  Also checking on the bypass air reporting.
> 
> Mike
> 
> 
> On 11 Jun 2006 at 8:38, eric_zhou1223 wrote:
> 
> > Hi all,
> > 
> > I am looking into the example file(v1.3) "HVACStandAloneERV_Economizer" 
> > and notice something.
> > The "OA HEAT RECOVERY 1:Heat Recovery Defrost Time Fraction" has a 
> > value 0.3 around, but the "OA HEAT RECOVERY 1:Heat Recovery Supply Air 
> > Bypass Mass Flow" is zero all the time, even after I changed the HRV 
> > type as "Plate". Could anyone explain this?
> > 
> > Besides, the SVG can not be seen. A warning says:
> > 
> > ERROR - COULD NOT COMPLETE DRAWING! Examine ERR file for possible 
> > explanation. Last error message is: "Diagram pieces not linked 
> > (upstream): OA HEAT RECOVERY 1"
> > 
> > Thank you.
> > Eric
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate
> folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press
> the
> > "search" button.
> >  
> > Yahoo! Groups Links
> > 
> > 
> > 
> >  
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/