[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: How do you disable modulation of opening factors?



The window opening with the temperature control option (ventilation control 
mode) is determined by the temperature difference between indoor and 
outdoors only. It is possible that a window is opened in a minute and closed 
at the next minute, because the minimum system time step is a minute. The 
AirflowNetwork model does not consider any opening duration.

I looked at your input file. The two opposite windows belong to two 
different zone. Since the window opening is determined by the temperature 
difference between a zone and outdoors, two windows will not open at the 
same time if two zones have different temperatures.

Although you have options to select a ventilation control mode, you only can 
select one of them, not both, such as constant and temperature control 
options. If yes, what is a logic?

Thanks.

Lixing Gu


----- Original Message ----- 
From: "colotupper" <kendra.tupper@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Thursday, September 07, 2006 11:16 AM
Subject: [EnergyPlus_Support] Re: How do you disable modulation of opening 
factors?


> Thanks for explaining that!
>
> It's a little strange that the decision of whether or not to open the
> windows occurs on a minute by minute basis (this is how it appeared
> when I output in detailed mode).  It would be nice if there was a
> control that could force the windows to be either open or closed for
> at least a half an hour (or something other time chunk) to avoid the
> unrealistic modelling of windows being opened and closed every minute
> based on temperature conditions.
>
> Also, I am trying to model cross ventilation, but the opposite windows
> are not always opening at the same times.  Is there any way to model
> ventilation with temperature control and force the windows to open
> simultaneously?  I am guessing this has to be done with the constant
> control mode and a schedule, but then the windows are opened
> regardless of the outdoor air temperatures.
>
> Thanks,
>
> Kendra
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>>
>> Kendra:
>>
>> What you have done is right to make all opening factors either 0 or 1.
>> Output results are also right at "timestep" report frequency.
>>
>> There are two timesteps used in EnergyPlus: zone time step and
> system time
>> step. The zone time step is your input from the TIMESTEP IN HOUR
> object. The
>> system time step is used internally and is determined by zone
> temperature
>> difference between previous timestep and current timestep. If the
> difference
>> is more than 0.3C, the system time step is shorter than the zone
> time step.
>> The AirflowNetwork model is performed at the system timestep level.
> If you
>> use "detailed" reprt frequency, you can see opening factors are
> either 0 or
>> 1.0. When "timestep" reprot frequncey is used, the opening factors
> are gived
>> as an average value over a zone timestep when system time step <
> zone time
>> step. That is why you see opening factors vary between 0 and 1.0.
>>
>> Please let me know if you have more concerns.
>>
>> Lixing Gu
>> Florida Solar Energy Center
>>
>> ----- Original Message ----- 
>> From: "colotupper" <kendra.tupper@...>
>> To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
>> Sent: Wednesday, September 06, 2006 9:12 PM
>> Subject: [EnergyPlus_Support] How do you disable modulation of opening
>> factors?
>>
>>
>> >I am simulating Natural Ventilation with Airflow Networks and my
>> > Ventilation Control Mode = Temperature.  I want to have only 2
>> > conditions: closed windows (opening factor = 0) and open windows
>> > (opening factor = 1).  I have set Limit Value on Multiplier for
>> > Modulating Venting Open Factor = 1, and all opening factors equal to 1
>> > as well.
>> >
>> > For some reason, when i output hourly results, my Opening Factor and
>> > Opening Factor Multiplier for Venting Modulation  vary between 0
> and 1.
>> >
>> > I read past messages about this problem and tried changing my
>> > timesteps and reporting frequency, but this had no effect.  Right now,
>> > I have my timestep set to 1 and my report frequency set to timestep.
>> > I also tried letting all of the fields default to disable the
>> > modulation, but this had no impact either.
>> >
>> > I am going to post this file - if anyone has any suggestion, I would
>> > greatly appreciate it!
>> >
>> > Thanks,
>> >
>> > Kendra
>> >
>> >
>> >
>> >
>> >
>> >
>> > The primary EnergyPlus web site is found at:
>> > http://www.energyplus.gov
>> >
>> > The group web site is:
>> > http://groups.yahoo.com/group/EnergyPlus_Support/
>> >
>> > Attachments are not allowed -- please post any files to the
> appropriate
>> > folder in the Files area of the Support Web Site.
>> >
>> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf
> and press
>> > the "search" button.
>> >
>> > Yahoo! Groups Links
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>>
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press 
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
> 




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/