[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Controls



Hello Fred,

Thanks for the response - it solves my problem - well done.

Tony

  -----Original Message-----
  From: fred buhl [mailto:wfbuhl@xxxxxxx]
  Sent: 18 September 2006 19:17
  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
  Subject: Re: [EnergyPlus_Support] Controls


  Tony,

  Take a look at System Availability Manager:Night Cycle. The InputOutput
  Reference
  describes this manager pretty well. It will do what you want to do.

  Fred Buhl

  tonybaxterhevacomp wrote:

  >Hello anyone,
  >
  >If I have a warm air system (fan, heater battery, supply ductwork)
  >operating in winter to warm a factory to 20 degC during the day, but I
  >want to avoid the temperature dropping below 12 degC overnight, can I
  >control the fan and heater so that it is normally off overnight but
  >comes on when room temperature drops below 12 degC?
  >
  >Many thanks
  >
  >Tony Baxter
  >
  >
  >
  >
  >
  >
  >The primary EnergyPlus web site is found at:
  >http://www.energyplus.gov
  >
  >The group web site is:
  >http://groups.yahoo.com/group/EnergyPlus_Support/
  >
  >Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
  >
  >EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
  >
  >Yahoo! Groups Links
  >
  >
  >
  >
  >
  >
  >
  >
  >
  >
  >


  


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/