Re: [EnergyPlus_Support] Heat exchanger and fancoil unit:4 pipe



No, and heat exchanger cannot be added to a fan coil unit.  

A close approximation would be a fan coil with no outside air plus an ENERGY 
RECOVERY VENTILATOR:STAND ALONE both serving the same zone.  Be sure to set the 
ENERGY RECOVERY VENTILATOR:STAND ALONE to run first for both heating and 
cooling so that the fan coil will "see" the impact of the ventilation air.  The 
key difference from the integrated HX is that the entering conditions to the 
fan coil cooling coil will be different, but overall the energy use should be 
very similar.

Mike


On 9 Jan 2007 at 18:04, Pedro Rodrigo wrote:

> Hi all:
> 
> Can I link a "HEAT EXCHANGER:AIR TO AIR:GENERIC" to the outside and exhaust air nodes of a "FANCOIL UNIT:4 PIPE"? If yes, what objects should I add to the 4 pipe fancoil standard definition?
> 
> Thanks in advance.
>  
> P.D.: I dont´t need to use supply air outlet temperature control nor frost control for the heat exchanger.
> 
> 
> Pedro Manuel Rodrigo Cruz
> Universidad de Jaén
> 
> 
> 
> __________________________________________________
> Correo Yahoo!
> Espacio para todos tus mensajes, antivirus y antispam ¡gratis! 
> Regístrate ya - http://correo.yahoo.es 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/