[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Uploading idf file



It is hard to answer your question, because I do not know what basis you are 
comparing to.  Some things I notice:

1.  This input file appears to model a single middle floor to represent several 
floors, but the zone multipliers are all 1.  So the loads only reflect a 
building with the area of 3 floors (not 7 or however many there are supposed to 
be).

2.  There are no internal gains (of course, this would decrease the heating 
loads).

3.  There is no ventilation air other than infiltration.  

4.  The south zones have large amounts of glass.

5.  The east and west ends of the building are buffered by unconditioned 
spaces.

Does this help?

Mike


On 5 Feb 2007 at 1:10, dimitris drougas wrote:

> I made uploaded the idf file the weather File is GRC_Athens_IWEC.epw. Very low annual zone/sys sensible Heating Energy
> 
> 
>  
> ____________________________________________________________________________________
> Now that's room service!  Choose from over 150,000 hotels
> in 45,000 destinations on Yahoo! Travel to find your fit.
> http://farechase.yahoo.com/promo-generic-14795097
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/