There is no known issue with COMPACT HVAC:ZONE:FAN COIL.  The example file 
CompactHVAC-5ZoneFanCoil.idf runs without error.  Something about your model is 
significantly different from the example file.  If you look at the expidf file, 
you will see the following fields in the cooling coil object:

COIL:Water:DetailedFlatCooling,

  autosize,   !- Fin Diameter {m}
  0.0015,     !- Fin Thickness {m}
  0.01445,    !- Tube Inside Diameter {m}
  0.0159,     !- Tube Outside Diameter {m}

Apparently the default value for "Tube Inside Diameter" is larger than the 
autosized value "Fin Diameter".  If you look at the eio output file, you will 
see what the autosized value was for "Fin Diameter".  The only solution I can 
suggest at this point is to copy the expidf file to a new file name.idf, and 
then edit the values for Tube Inside Diameter and Tube Outside Diameter to be 
small enough to run without error.

In the next release, we plan to make the simpler cooling coil model an option, 
which should eliminate this problem.  Likewise, the detailed cooling coil 
should be able to ensure that the fin size is not autosized to be smaller than 
the tubes.

Mike



On 20 Mar 2007 at 16:22, dust_broom wrote:

> Dear all
> 
> I'm trying to simulate a simple water based fan coil system. To 
> simplify the input I'm using the Compact HVAC module. However, every 
> time I run the .idf file to obtain the .expidf file, I get this error 
> message: 
> 
> ** Severe  ** InitWaterCoil: Detailed Flat Fin Coil, TubetoFinDiamRatio 
> > 1.0, [1.2544]
> 
> Is there any known issue with the Compact HVAC:ZOne:Fancoil ?! In fact 
> this is not the first time I use this module, and I'm always getting 
> this same error message.
> 
> Regards
> 
> Emanuel Sá
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/