[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] A Question about sensible heating and cooling rate for one zone.



It is most unlikely that this would happen during "detailed" 
reporting.  However it is quite likely during timestep (i.e. Zone 
TimeStep) or hourly reporting.

The HVAC time step automatically reduces itself below the zone time 
step to get to convergence.

Read about the TimeStep in Hour and System Convergence limits as well 
as searching the documentation for "timestep".

At 03:03 PM 4/9/2007, xjtu.guowei wrote:
> >From the results of one of my simulations, I have found that during
>some timesteps for one zone the sensible heating and sensible cooling
>rate are both greater than zero.


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/