[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

AW: AW: Re: [EnergyPlus_Support] Interior Blind - BlockBeamSolar



 Rob,
I compared my file with the example and solution is that
the slat separation was greater as the slat width.
Thanks.
 
Arno

  _____  

Von: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Im Auftrag von Rob Hitchcock
Gesendet: Mittwoch, 25. April 2007 01:14
An: EnergyPlus_Support@xxxxxxxxxxxxxxx
Betreff: Re: AW: Re: [EnergyPlus_Support] Interior Blind - BlockBeamSolar



Arno,

I have successfully used the example file "PurchAirWindowBlind.idf", 
modified to match your desired control strategy, for both Interior and 
Exterior Blinds. You might use that example file as a starting point 
for debugging your input. Note that your 2003_Shaded11 construction 
object needs to switch the Material:WindowBlind layer from the inside, 
for Interior Blind, to the outside for Exterior Blind.

Rob
========
arno.dentel@ <mailto:arno.dentel%40fh-nuernberg.de> fh-nuernberg.de wrote:

> Rob,
>
> thank you for your response.
> The radiation on the window is several times over the setpoint of 180 
> W/m². I printed, also,
> out the output "shading device is on". And it is on (1).
> I calculated the same example with an exterior blind. And it works 
> well. But not yet for
> the interior blind. Below I listed the material properties for the 
> interior blind.
> Perhaps you can have a look on this.
> Thanks, Arno
>
> MATERIAL:WINDOWBLIND,
> Typ11, !- Name
> HORIZONTAL, !- Slat orientation
> 0.035, !- Slat width {m}
> 0.04000, !- Slat separation {m}
> 0.001, !- Slat thickness {m}
> 45.0, !- Slat angle {deg}
> 221.0, !- Slat conductivity {W/m-K}
> 0.1, !- Slat beam solar transmittance
> 0.4, !- Slat beam solar reflectance, front side
> 0.4, !- Slat beam solar reflectance, back side
> 0.1, !- Slat diffuse solar transmittance
> 0.4, !- Slat diffuse solar reflectance, front side
> 0.4, !- Slat diffuse solar reflectance, back side
> 0.1, !- Slat beam visible transmittance
> 0.4, !- Slat beam visible reflectance, front side
> 0.4, !- Slat beam visible reflectance, back side
> 0.1, !- Slat diffuse visible transmittance
> 0.4, !- Slat diffuse visible reflectance, front side
> 0.4, !- Slat diffuse visible reflectance, back side
> 0.0, !- Slat IR (thermal) hemispherical transmittance
> 0.3, !- Slat IR (thermal) hemispherical emissivity, front side
> 0.3, !- Slat IR (thermal) hemispherical emissivity, back side
> 0.100, !- Blind-to-glass distance {m}
> 1.0, !- Blind top opening multiplier
> 1.0, !- Blind bottom opening multiplier
> 1.0, !- Blind left-side opening multiplier
> 1.0, !- Blind right-side opening multiplier
> 0, !- Minimum Slat Angle {deg}
> 180; !- Maximum Slat Angle {deg}
>
> --- Originalnachricht ---
> > Arno,
> > There are several factors interacting under your desired control
> > strategy. You are deploying your interior blind only when beam
> > +
> > diffuse solar incident on the window is > 180 W/m2. You should
> > output
> > this variable so that you can assure that your blind is being
> > properly
> > deployed. Also, the BlockBeamSolar control uses the input data
> > in the
> > Material:WindowBlind object, which you have not included in
> > your email
> > message. The Material:WindowBlind construction must be complete
> > and
> > accurate enough for EnergyPlus to determine the appropriate
> > slat angle
> > to block beam when the blind is deployed.
> > Rob Hitchcock
> > =========
> > Arno Dentel wrote:
> > > Dear Users.
> > >
> > > I simulate a simple room with an interior blind. The control type 
> of the
> > > slat angles is: BlockBeamSolar.
> > > But in the output (FENSTER_1:Window Blind Slat Angle 
> [deg](TimeStep)) is
> > > always 0.
> > > At the end of my mail you can find the specifications of the window
> > > control
> > > object out of my idf file.
> > > Has any body an idea?
> > >
> > > Best Regards,
> > > Arno
> > >
> > > !- =========== ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB
> > > ===========
> > >
> > > Surface:HeatTransfer:Sub,
> > > Fenster_1, !- User Supplied Surface Name
> > > WINDOW, !- Surface Type
> > > 2003, !- Construction Name of the Surface
> > > Wand_2, !- Base Surface Name
> > > , !- OutsideFaceEnvironment Object
> > > 0.0, !- View Factor to Ground
> > > ysun_1_11, !- Name of shading control
> > > , !- WindowFrameAndDivider Name
> > > 1, !- Multiplier
> > > 4, !- Number of Surface Vertex Groups -- Number of
> > > (X,Y,Z) groups in this surface
> > > 0.32260, !- Vertex 1 X-coordinate {m}
> > > 0.00000, !- Vertex 1 Y-coordinate {m}
> > > 0.95517, !- Vertex 1 Z-coordinate {m}
> > > 3.62740, !- Vertex 2 X-coordinate {m}
> > > 0.00000, !- Vertex 2 Y-coordinate {m}
> > > 0.95517, !- Vertex 2 Z-coordinate {m}
> > > 3.62740, !- Vertex 3 X-coordinate {m}
> > > 0.00000, !- Vertex 3 Y-coordinate {m}
> > > 2.54483, !- Vertex 3 Z-coordinate {m}
> > > 0.32260, !- Vertex 4 X-coordinate {m}
> > > 0.00000, !- Vertex 4 Y-coordinate {m}
> > > 2.54483; !- Vertex 4 Z-coordinate {m}
> > >
> > > !- =========== ALL OBJECTS IN CLASS: WINDOWSHADINGCONTROL ===========
> > >
> > > WindowShadingControl,
> > > ysun_1_11, !- User Supplied Shading Control Name
> > > InteriorBlind, !- Shading Type
> > > 2003_Shaded11, !- Name of construction with shading
> > > OnIfHighSolarOnWindow, !- Shading Control Type
> > > , !- Schedule Name
> > > 180.00, !- SetPoint {W/m2, W or deg C}
> > > No, !- Shading Control Is Scheduled
> > > No, !- Glare Control Is Active
> > > , !- Material Name of Shading Device
> > > BlockBeamSolar, !- Type of Slat Angle Control for Blinds
> > > ; !- Slat Angle Schedule Name
> > >
> > > ______________________________________________________
> > >
> > > Arno Dentel - MEng, Dipl.-Ing. (FH)
> > > Georg-Simon-Ohm Fachhochschule Nürnberg
> > > Institut für Energie und Gebäude - ieg
> > > Keßlerplatz 12
> > > 90489 Nürnberg
> > >
> > > Tel: +49 - 911 - 5880 -1846
> > > Fax: +49 - 911 - 5880 -5846
> > >
> > > E-Mail: arno.dentel@ <mailto:arno.dentel%40fh-nuernberg.de>
fh-nuernberg.de 
> <mailto:arno.dentel%40fh-nuernberg.de> 
> (mailto:arno.dentel%40fh-nuernberg.de) 
> <mailto:arno.dentel%40fh-nuernberg.de>
> > > web: www.ieg.fh-nuernberg.de <http://www.ieg.
<http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/ 
> <http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/>
(http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/ 
> <http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/>)
> > > <http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/
<http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/> 
> (http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/
<http://www.ieg. <http://www.ieg.fh-nuernberg.de/> fh-nuernberg.de/>)>>
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >
> > --
> > Robert J. Hitchcock, Ph.D.
> > Lawrence Berkeley National Laboratory
> > 1 Cyclotron Road, Mailstop 90-3111
> > Berkeley, CA 94720
> > RJHitchcock@ <mailto:RJHitchcock%40lbl.gov> lbl.gov
<mailto:RJHitchcock%40lbl.gov> 
> (mailto:RJHitchcock%40lbl.gov)
> > 530.295.9433 (telecommute office)
> > [Non-text portions of this message have been removed]
> >
>
> 

[Non-text portions of this message have been removed]



 


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/