[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Parametric Study and Autosizing?



If the energy conservation measures affect the building's zone loads, 
then the autosized zone design
flow rates will change - and downstream the boiler, chiller, fan etc. An 
example would be a different
type of window - that would affect the autosizing results.

Fred Buhl

noelcrrl wrote:
> Dear all,
>
> I have completed a baseline building in EnergyPlus.  All of the 
> equipment in this building was autosized.  I plan to model multiple 
> energy conservation measures using this baseline building.  I am 
> concerned that with each simulation run where I model an energy 
> conservation measure (add it to the baseline model), the capacity of 
> the building equipment (boiler, chiller, fan, etc.) will change. Do I 
> have to hard size the equipment (boiler, chiller, fan, etc.), based on 
> the values from the baseline model's EIO, for the runs where I model 
> these measures?  Should I expect the "autosized" capacity of the 
> equipment to change with each run?  Or, should I expect the "autosized" 
> values to remain the same with each run?  What is the protocol?
>
> Thanks in advance,
>
> Noel
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/