[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] interior blinds



Placing blinds and/or shades on the interior of a window will not stop 
solar gains from entering the zone.  Solar will still be transmitted 
through the window and will warm up the blind/shade surface, which is 
inside the zone.  Some solar will be reflected back out the window, but 
this will not reliably lower the overall solar gains relative to a 
window without an interior blind or shade.

Try placing the blind/shade on the exterior of the window for comparison.

Rob
=======
yiqunpan wrote:

> I made a model to simulate the heat transfer from the evenlope. In the
> model I used interior blinds for windows as well as without blinds. I
> thought that the cooling loads through the envelope due to solar heat
> gain should be higher without blinds than with blinds, but the results
> show that in some time (e.g. early morning on east facade and late
> afternoon on west facade) it is higher with blinds. What is the reason
> exactly? I also tried interior shade, but the results are similar.
>
>  





[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/