[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] condfd Vs ctf



thanks for your help,i will try it again

"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:          This is a known issue (see #7236 in Known_Issues-V2-0-0.htm). The problem does 
not occur in all models. We are investigating why and when it happens. One 
thing we do know is that Material:Regular-R can cause problems. So, one thing 
to try is to replace all Material:Regular-R objects with equivalent 
Material:Regular.

Mike

On 6 Jun 2007 at 4:24, basill_xw wrote:

> I will simulate a building containing PCMs.So I would like to test 
> energy+ calculations using CondFD instead of CTF for a buliding without 
> PCMs.
> I created a buliding model(about 10 thermal zones) wihtout heating and 
> cooling equipments in 
> designbuilder V1.3. First I finished the simulation with CTF algorithm
> (time step in hour is 6).Sencond I finished the simulation with Condfd
> (time step in hour is 60). And both algorithms reach convergence during 
> the warmup days.
> Then I compared the two results,there is a big difference between the 
> two results. The amplitude of indoor temperature(from Condfd algorithm)
> is much smaller than the amplitue of indoor temperature(from CTF 
> algorithm).
> And I have done the same work in e+ v2.0. There is the same problem.
> 
> Does anybody know why ?
> thank for your help in advance!
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 

========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support 
EnergyPlus-Support@xxxxxxxx



         

 _______________________________________
 辣茩妏蚚閉湮⺍講捇誥蚘眊 
 http://cn.mail.yahoo.com 

[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/