[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Re: *.Rvi File Question



Hi,

We are working on the same issue. We wrote "imf" and "epg" files for a
parametric study. We wrote a batch file to run RunReadvarseso for each of the
parametric cases to convert "eso" files to "csv" files and we are able to get
"eso" output files for each parametric case. Then we could import 
various *.csv
sets into excel worksheets to create the reports for our goal by using batch
files. The problem is that the results in "Table.csv" files which are in kWh
seems correct but when converting the eso files into "csv" files using
RunReadeso.bat, the results in Joule are not correct. A decimal seperation
problem occurred after we added the SCHEDULE COMPACT lines and related REPORT
VARIABLE lines into imf files for getting the parametric results in the 
defined
order. We couldn?t solve the problem occurred in the final csv output files.

What can be the reason of this problem?

Thanks in advance

Aslihan



Quoting "Crawley, Drury" <Drury.Crawley@xxxxxxxxxx>:

> Mike,
>
> I'm doing exactly that--creating individual RVIs for different outputs
> and meter results. It's fairly simple to create a modified batch file to
> run this--after the simulation is completed.  I can share my modified
> batch file if you're interested.  I have about 20 separate RVIs and MVIs
> (of course tailored to the IDFs I'm running).
>
> Dru
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Micheal
> Sent: Friday, July 06, 2007 4:07 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: *.Rvi File Question
>
>
>
> Thank for the quick response. I thought this would be the case.
>
> I have a follow-up question. Can you run RunReadvarsESO.exe multiple
> times? For example have several RVI files with "sets" of variables
> like environment, walls, zones, systems and report to multiple *.csv
> files. Also could use separate time frames in the *.rvi files. Using
> this methodology I would hope I could import the various *.csv sets
> into excel on different worksheets and use the data to create
> reports in my own format.
>
> A second question is do you know what happens if the *.rvi variable
> is not present? For example if I where to enforce a generic naming
> convention (such as wall1, wall2, ...) and not use all the names.
> Would I just get the warning "The following variable were requested
> but not generated". Do you know if it would "skip" the column to
> maintain an absolute relationship or delete the non-existent
> variable column to create a compact table with no "empty" columns?
>
> Thanks in advance,
>
> Mike
>
> PS: I have and use XESOView which I find to be a very good program.
> The problem I run into is that it doesn't allow looking at (charting
> or reporting) multiple variables at the same time. Also, the company
> I work for has quite a few "oldtimers" which I need to produce
> outputs formatted in similar ways to their currently used methods
> (CHVAC, Trace, and even hand calculated CLTD!) so that they can
> better understand what is going on. The buildings we tend to model
> are simple and very similar to one another (warehouses, maintenance
> buildings, mechanical buildings, etc. for electric power plants). I
> plan on masking most of the input and output of EPlus in a
> more "user friendly" format using Excel hense all the questions
> above.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Linda Lawrie
> <lklawrie@...> wrote:
>>
>> You must use the rvi file for this purpose. Whatever you put in
>> report variables, get shoved out to the eso file (or in case of
>> meters also the .mtr file) as they "come up" in the simulation.
> The
>> actual order for that would be shown in the first part of the eso
>> file (before the part that says "End of Data Dictionary".
>>
>> In the rvi file, you can either specify the generic form of the
>> report variable, e.g.:
>>
>> Zone/Sys Air Temperature
>> Zone/Sys Sensible Heating Energy
>> Zone/Sys Sensible Cooling Energy
>>
>> or be really specific:
>> Zone 1:Zone/Sys Air Temperature
>> Zone 1:Zone/Sys Sensible Heating Energy
>> Zone 1:Zone/Sys Sensible Cooling Energy
>>
>> The first instance will give you all the zones, Zone/Sys Air
>> Temperature, followed by all the Zones, Zone/Sys Sensible Heating
>> Energy, etc. whereas the second will put the 3 variables by zone.
>>
>> There are also ways of only getting out the hourly or monthly
> values
>> in a csv file even though the eso file may contain multiple hourly
>> and monthly mixed.
>>
>> There is also the utility XESOView (not part of the EnergyPlus
>> install) but you can find out about it on either the yahoo groups
>> website or the energyplus.gov website. I don't know if it would
> be
>> suitable for your purposes or not.
>>
>>
>> Linda
>>
>> EnergyPlus WebSite: http://www.energyplus.gov
> <http://www.energyplus.gov>
>> Owner: EnergyPlus_Support list
>> Member: EnergyPlus Development Team
>>
>>
>>
>> [Non-text portions of this message have been removed]
>>
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>



----------------------------------------------------------------
This message was sent using IMP, the Internet Messaging Program.



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/