The cooling is operating, see PurchasedCooling:Facility.  Because the chilled 
water loop is served by PURCHASED:CHILLED WATER, there will be no 
Cooling:Electricity consumption.  Some cooling is occuring, but it is not 
enough.  Report the chilled water outlet temperature.  If this is not meeting 
setpoint, the the purchased chilled water is too small.  If the chilled water 
setpoint is being met, report the air temperature at the air loop outlet.  If 
this is not meeting setpoint, then the chilled water coil may not be large 
enough.  If the air temperature is OK, then the airflows to the zones may not 
be large enough.

Mike


On 9 Jul 2007 at 12:37, love9787m wrote:

> Hi,
> 
> Currently, simulating the 18story building served by Desiccant CV.
> I've checked all parts of the objects and field.
> Input values and nodes, nodes connection, everything is OK. 
> But Cooling isn't operating.
> Indoor radiant temperature is nearly 40~50C.
> In the Report meter, The value of Cooling:electricity is 0.
> It means that cooling isn't operating.
> I'll upload my idf file.
> Please check the faults and mistakes of my file.
> Thank you inadvance for your help.
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/