[EnergyPlus_Support] trouble with defining blinds



hi
I am trying to make cooling load calculation of a zone having two 
opening one of which has exterior blind in front of it. Windows are 
always open. 
I can not create the right idf file. It always shows 3 severe 
errors. 
I don't know creating schedules so I copy schedules from example 
files. Can anyone give some help to define my blinds. I will attach 
my file
thank you

!-Generator IDFEditor 1.27 'current version of IDFEditor - less than 
1 is a beta

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are 
generated automatically.
!-      Use '!' comments if they need to be retained when using the 
IDFEditor.


!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========

VERSION,
    1.4;                     !- Version Identifier


!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========

BUILDING,
    Ofis ,                   !- Building Name
    0,                       !- North Axis {deg}
    City,                    !- Terrain
    0.04,                    !- Loads Convergence Tolerance Value
    0.4,                     !- Temperature Convergence Tolerance 
Value {deltaC}
    FullInteriorAndExteriorWithReflections,  !- Solar Distribution
    30;                      !- Maximum Number of Warmup Days


!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP IN HOUR ===========

TIMESTEP IN HOUR,
    4;                       !- Time Step in Hour


!-   ===========  ALL OBJECTS IN CLASS: INSIDE CONVECTION ALGORITHM 
===========

INSIDE CONVECTION ALGORITHM,
    Detailed;                !- Algorithm


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE CONVECTION ALGORITHM 
===========

OUTSIDE CONVECTION ALGORITHM,
    Detailed;                !- Algorithm


!-   ===========  ALL OBJECTS IN CLASS: SOLUTION ALGORITHM 
===========

SOLUTION ALGORITHM,
    CTF;                     !- SolutionAlgo


!-   ===========  ALL OBJECTS IN CLASS: SHADOWING CALCULATIONS 
===========

SHADOWING CALCULATIONS,
    20;                      !- Period_for_calculations


!-   ===========  ALL OBJECTS IN CLASS: ZONE VOLUME CAPACITANCE 
MULTIPLIER ===========

ZONE VOLUME CAPACITANCE MULTIPLIER,
    1;                       !- Capacitance Multiplier


!-   ===========  ALL OBJECTS IN CLASS: RUN CONTROL ===========

RUN CONTROL,
    No,                      !- Do the zone sizing calculation
    No,                      !- Do the system sizing calculation
    No,                      !- Do the plant sizing calculation
    No,                      !- Do the design day simulations
    Yes;                     !- Do the weather file simulation


!-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========

RunPeriod,
    8,                       !- Begin Month
    21,                      !- Begin Day Of Month
    8,                       !- End Month
    21,                      !- End Day Of Month
    ,                        !- Day Of Week For Start Day
    ,                        !- Use WeatherFile Holidays/Special Days
    ,                        !- Use WeatherFile DaylightSavingPeriod
    ,                        !- Apply Weekend Holiday Rule
    ,                        !- Use WeatherFile Rain Indicators
    ,                        !- Use WeatherFile Snow Indicators
    1;                       !- Number of years of simulation

RunPeriod,
    2,                       !- Begin Month
    21,                      !- Begin Day Of Month
    2,                       !- End Month
    21,                      !- End Day Of Month
    ,                        !- Day Of Week For Start Day
    ,                        !- Use WeatherFile Holidays/Special Days
    ,                        !- Use WeatherFile DaylightSavingPeriod
    ,                        !- Apply Weekend Holiday Rule
    ,                        !- Use WeatherFile Rain Indicators
    ,                        !- Use WeatherFile Snow Indicators
    1;                       !- Number of years of simulation


!-   ===========  ALL OBJECTS IN CLASS: LOCATION ===========

Location,
    ISTANBUL_TUR Design_Conditions,  !- LocationName
    40.97,                   !- Latitude {deg}
    28.82,                   !- Longitude {deg}
    2.00,                    !- TimeZone {hr}
    37.00;                   !- Elevation {m}


!-   ===========  ALL OBJECTS IN CLASS: DESIGNDAY ===========

DesignDay,
    ISTANBUL Ann Htg Wind 99% Condns WS=>MCDB,  !- DesignDayName
    2,                       !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Temperature Range {deltaC}
    2,                       !- Humidity Indicating Conditions at 
Max Dry-Bulb
    100881.,                 !- Barometric Pressure {Pa}
    11.3,                    !- Wind Speed {m/s}
    0,                       !- Wind Direction {deg}
    0.00,                    !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    21,                      !- Day Of Month
    2,                       !- Month
    WinterDesignDay,         !- Day Type
    0,                       !- Daylight Saving Time Indicator
    Wet-Bulb;                !- Humidity Indicating Type

DesignDay,
    ISTANBUL Ann Clg .4% Condns DB=>MWB,  !- DesignDayName
    31.1,                    !- Maximum Dry-Bulb Temperature {C}
    7.9,                     !- Daily Temperature Range {deltaC}
    21.5,                    !- Humidity Indicating Conditions at 
Max Dry-Bulb
    100881.,                 !- Barometric Pressure {Pa}
    6,                       !- Wind Speed {m/s}
    30,                      !- Wind Direction {deg}
    1.00,                    !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    21,                      !- Day Of Month
    8,                       !- Month
    SummerDesignDay,         !- Day Type
    0,                       !- Daylight Saving Time Indicator
    Wet-Bulb;                !- Humidity Indicating Type


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR ===========

MATERIAL:REGULAR,
    PLASTER - CEMENT SA 3 / 8 IN,  !- Name
    Smooth,                  !- Roughness
    0.002,                   !- Thickness {m}
    0.7200000,               !- Conductivity {W/m-K}
    1858.140,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.7800000,               !- Absorptance:Solar
    0.7800000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    BRICK - COMMON 8 IN,     !- Name
    Rough,                   !- Roughness
    0.19,                    !- Thickness {m}
    0.7200000,               !- Conductivity {W/m-K}
    1922.210,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.7000000,               !- Absorptance:Solar
    0.7000000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    IN76 - 2 IN PREFORMED MINERAL BOARD,  !- Name
    Smooth,                  !- Roughness
    0.060000001,             !- Thickness {m}
    3.9999999E-02,           !- Conductivity {W/m-K}
    240.2700,                !- Density {kg/m3}
    710.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.5000000,               !- Absorptance:Solar
    0.5000000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    E10 - 1 IN GYP PLASTER SAND AGG,  !- Name
    Smooth,                  !- Roughness
    2.0000000E-02,           !- Thickness {m}
    0.8200000,               !- Conductivity {W/m-K}
    800.9200,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.9200000,               !- Absorptance:Solar
    0.9200000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    FINISH FLOORING - TILE 1 / 16 IN,  !- Name
    Smooth,                  !- Roughness
    0.005,                   !- Thickness {m}
    0.1700000,               !- Conductivity {W/m-K}
    1922.210,                !- Density {kg/m3}
    1250.000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.5000000,               !- Absorptance:Solar
    0.5000000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    B6 - 2 IN DENSE INSULATION,  !- Name
    VeryRough,               !- Roughness
    0.08,                    !- Thickness {m}
    3.9999999E-02,           !- Conductivity {W/m-K}
    91.30000,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.5000000,               !- Absorptance:Solar
    0.5000000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    C18 - 1.25 IN LIGHT WEIGHT CONCRETE,  !- Name
    MediumRough,             !- Roughness
    0.03,                    !- Thickness {m}
    0.1200000,               !- Conductivity {W/m-K}
    480.5500,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.2000000,               !- Absorptance:Solar
    0.2000000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    C14 - 4 IN LW CONCRETE,  !- Name
    MediumRough,             !- Roughness
    0.1000000,               !- Thickness {m}
    0.1700000,               !- Conductivity {W/m-K}
    640.7300,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.6500000,               !- Absorptance:Solar
    0.6500000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    C5 - 4 IN HW CONCRETE,   !- Name
    MediumRough,             !- Roughness
    0.15,                    !- Thickness {m}
    1.720000,                !- Conductivity {W/m-K}
    2242.580,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.6500000,               !- Absorptance:Solar
    0.6500000;               !- Absorptance:Visible

MATERIAL:REGULAR,
    C13 - 6 IN HW CONCRETE,  !- Name
    MediumRough,             !- Roughness
    0.1500000,               !- Thickness {m}
    1.720000,                !- Conductivity {W/m-K}
    2242.580,                !- Density {kg/m3}
    830.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Absorptance:Thermal
    0.6500000,               !- Absorptance:Solar
    0.6500000;               !- Absorptance:Visible


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGLASS 
===========

MATERIAL:WINDOWGLASS,
    GLASS - CLEAR PLATE 1 / 4 IN,  !- Name
    SpectralAverage,         !- Optical Data Type
    ,                        !- Name of Window Glass Spectral Data 
Set
    6.0000001E-03,           !- Thickness {m}
    0.7750000,               !- Solar Transmittance at Normal 
Incidence
    7.1000002E-02,           !- Solar Reflectance at Normal 
Incidence: Front Side
    7.1000002E-02,           !- Solar Reflectance at Normal 
Incidence: Back Side
    0.8810000,               !- Visible Transmittance at Normal 
Incidence
    7.9999998E-02,           !- Visible Reflectance at Normal 
Incidence: Front Side
    7.9999998E-02,           !- Visible Reflectance at Normal 
Incidence: Back Side
    0,                       !- IR Transmittance at Normal Incidence
    0.8400000,               !- IR Hemispherical Emissivity: Front 
Side
    0.8400000,               !- IR Hemispherical Emissivity: Back 
Side
    0.9000000;               !- Conductivity {W/m-K}


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWBLIND 
===========

MATERIAL:WINDOWBLIND,
    BLIND WITH LOW REFLECTIVITY SLATS,  !- Name
    HORIZONTAL,              !- Slat orientation
    0.38625,                 !- Slat width {m}
    0.386,                   !- Slat separation {m}
    0.00025,                 !- Slat thickness {m}
    90,                      !- Slat angle {deg}
    221,                     !- Slat conductivity {W/m-K}
    0.0,                     !- Slat beam solar transmittance
    0.2,                     !- Slat beam solar reflectance, front 
side
    0.2,                     !- Slat beam solar reflectance, back 
side
    0.0,                     !- Slat diffuse solar transmittance
    0.2,                     !- Slat diffuse solar reflectance, 
front side
    0.2,                     !- Slat diffuse solar reflectance, back 
side
    0.0,                     !- Slat beam visible transmittance
    0.2,                     !- Slat beam visible reflectance, front 
side
    0.2,                     !- Slat beam visible reflectance, back 
side
    0.0,                     !- Slat diffuse visible transmittance
    0.2,                     !- Slat diffuse visible reflectance, 
front side
    0.2,                     !- Slat diffuse visible reflectance, 
back side
    0.0,                     !- Slat IR (thermal) hemispherical 
transmittance
    0.9,                     !- Slat IR (thermal) hemispherical 
emissivity, front side
    0.9,                     !- Slat IR (thermal) hemispherical 
emissivity, back side
    0.327953,                !- Blind-to-glass distance {m}
    0.5,                     !- Blind top opening multiplier
    0.5,                     !- Blind bottom opening multiplier
    0.5,                     !- Blind left-side opening multiplier
    0.5,                     !- Blind right-side opening multiplier
    0,                       !- Minimum Slat Angle {deg}
    90;                      !- Maximum Slat Angle {deg}


!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========

CONSTRUCTION,
    DUVAR,                   !- Name
    PLASTER - CEMENT SA 3 / 8 IN,  !- Outside Layer
    IN76 - 2 IN PREFORMED MINERAL BOARD,  !- Layer #2
    BRICK - COMMON 8 IN,     !- Layer #3
    E10 - 1 IN GYP PLASTER SAND AGG;  !- Layer #4

CONSTRUCTION,
    ZEMÝN DOSEME,            !- Name
    C5 - 4 IN HW CONCRETE,   !- Outside Layer
    C14 - 4 IN LW CONCRETE,  !- Layer #2
    C18 - 1.25 IN LIGHT WEIGHT CONCRETE,  !- Layer #3
    B6 - 2 IN DENSE INSULATION,  !- Layer #4
    C18 - 1.25 IN LIGHT WEIGHT CONCRETE,  !- Layer #5
    FINISH FLOORING - TILE 1 / 16 IN;  !- Layer #6

CONSTRUCTION,
    CATI,                    !- Name
    B6 - 2 IN DENSE INSULATION,  !- Outside Layer
    C13 - 6 IN HW CONCRETE,  !- Layer #2
    E10 - 1 IN GYP PLASTER SAND AGG;  !- Layer #3

CONSTRUCTION,
    ARA KAT TAVAN,           !- Name
    FINISH FLOORING - TILE 1 / 16 IN,  !- Outside Layer
    C13 - 6 IN HW CONCRETE,  !- Layer #2
    E10 - 1 IN GYP PLASTER SAND AGG;  !- Layer #3

CONSTRUCTION,
    ARA KAT DOSEME,          !- Name
    E10 - 1 IN GYP PLASTER SAND AGG,  !- Outside Layer
    C13 - 6 IN HW CONCRETE,  !- Layer #2
    FINISH FLOORING - TILE 1 / 16 IN;  !- Layer #3

CONSTRUCTION,
    DUVAR2,                  !- Name
    E10 - 1 IN GYP PLASTER SAND AGG,  !- Outside Layer
    BRICK - COMMON 8 IN,     !- Layer #2
    E10 - 1 IN GYP PLASTER SAND AGG;  !- Layer #3

CONSTRUCTION,
    WIN-CON-SINGLEPANE,      !- Name
    GLASS - CLEAR PLATE 1 / 4 IN;  !- Outside Layer

CONSTRUCTION,
    WIN-CON-SINGLEPANE WITH EXTERIOR BLIND,  !- Name
    GLASS - CLEAR PLATE 1 / 4 IN,  !- Outside Layer
    BLIND WITH LOW REFLECTIVITY SLATS;  !- Layer #2


!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========

ZONE,
    ofis-zone1,              !- Zone Name
    0,                       !- Relative North (to building) {deg}
    0,                       !- X Origin {m}
    0,                       !- Y Origin {m}
    0,                       !- Z Origin {m}
    1,                       !- Type
    1,                       !- Multiplier
    0,                       !- Ceiling Height {m}
    0;                       !- Volume {m3}


!-   ===========  ALL OBJECTS IN CLASS: SURFACEGEOMETRY ===========

SurfaceGeometry,
    LowerLeftCorner,         !- SurfaceStartingPosition
    CW,                      !- VertexEntry
    WorldCoordinateSystem;   !- CoordinateSystem


!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER 
===========

Surface:HeatTransfer,
    ARKA DUVAR,              !- User Supplied Surface Name
    WALL,                    !- Surface Type
    DUVAR2,                  !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    ARKA DUVAR,              !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    4.56,                    !- Vertex 1 X-coordinate {m}
    5.05,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    4.56,                    !- Vertex 2 X-coordinate {m}
    5.05,                    !- Vertex 2 Y-coordinate {m}
    4.05,                    !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    5.05,                    !- Vertex 3 Y-coordinate {m}
    4.05,                    !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    5.05,                    !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
    SOL YAN DUVAR,           !- User Supplied Surface Name
    WALL,                    !- Surface Type
    DUVAR2,                  !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    SOL YAN DUVAR,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    5.05,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    5.05,                    !- Vertex 2 Y-coordinate {m}
    4.05,                    !- Vertex 2 Z-coordinate {m}
    0,                       !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    4.05,                    !- Vertex 3 Z-coordinate {m}
    0,                       !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
    SAG YAN DUVAR,           !- User Supplied Surface Name
    WALL,                    !- Surface Type
    DUVAR2,                  !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    SAG YAN DUVAR,           !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    4.56,                    !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    4.56,                    !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    4.05,                    !- Vertex 2 Z-coordinate {m}
    4.56,                    !- Vertex 3 X-coordinate {m}
    5.05,                    !- Vertex 3 Y-coordinate {m}
    4.05,                    !- Vertex 3 Z-coordinate {m}
    4.56,                    !- Vertex 4 X-coordinate {m}
    5.05,                    !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
    ON DUVAR,                !- User Supplied Surface Name
    WALL,                    !- Surface Type
    DUVAR,                   !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ON DUVAR DIS YUZEY,      !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    0,                       !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    4.05,                    !- Vertex 2 Z-coordinate {m}
    4.56,                    !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    4.05,                    !- Vertex 3 Z-coordinate {m}
    4.56,                    !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
    DOSEME,                  !- User Supplied Surface Name
    FLOOR,                   !- Surface Type
    ARA KAT DOSEME,          !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    DOSEME,                  !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    0,                       !- Vertex 1 X-coordinate {m}
    5.05,                    !- Vertex 1 Y-coordinate {m}
    0.0,                     !- Vertex 1 Z-coordinate {m}
    0.000000,                !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0.0,                     !- Vertex 2 Z-coordinate {m}
    4.56,                    !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0.0,                     !- Vertex 3 Z-coordinate {m}
    4.56,                    !- Vertex 4 X-coordinate {m}
    5.05,                    !- Vertex 4 Y-coordinate {m}
    0.0;                     !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
    TAVAN,                   !- User Supplied Surface Name
    CEILING,                 !- Surface Type
    ARA KAT TAVAN,           !- Construction Name of the Surface
    ofis-zone1,              !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    TAVAN,                   !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    0.000000,                !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    4.05,                    !- Vertex 1 Z-coordinate {m}
    0.000000,                !- Vertex 2 X-coordinate {m}
    5.05,                    !- Vertex 2 Y-coordinate {m}
    4.05,                    !- Vertex 2 Z-coordinate {m}
    4.56,                    !- Vertex 3 X-coordinate {m}
    5.05,                    !- Vertex 3 Y-coordinate {m}
    4.05,                    !- Vertex 3 Z-coordinate {m}
    4.56,                    !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    4.05;                    !- Vertex 4 Z-coordinate {m}


!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB 
===========

Surface:HeatTransfer:Sub,
    Zn001:Arkaduvar-pencere, !- User Supplied Surface Name
    WINDOW,                  !- Surface Type
    WIN-CON-SINGLEPANE,      !- Construction Name of the Surface
    ARKA DUVAR,              !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5,                     !- View Factor to Ground
    ,                        !- Name of shading control
    ,                        !- WindowFrameAndDivider Name
    1,                       !- Multiplier
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    4.32999,                 !- Vertex 1 X-coordinate {m}
    5.05,                    !- Vertex 1 Y-coordinate {m}
    2.175,                   !- Vertex 1 Z-coordinate {m}
    4.32999,                 !- Vertex 2 X-coordinate {m}
    5.05,                    !- Vertex 2 Y-coordinate {m}
    2.675,                   !- Vertex 2 Z-coordinate {m}
    0.23001,                 !- Vertex 3 X-coordinate {m}
    5.05,                    !- Vertex 3 Y-coordinate {m}
    2.675,                   !- Vertex 3 Z-coordinate {m}
    0.23001,                 !- Vertex 4 X-coordinate {m}
    5.05,                    !- Vertex 4 Y-coordinate {m}
    2.175;                   !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer:Sub,
    Zn001:Onduvarpencere,    !- User Supplied Surface Name
    WINDOW,                  !- Surface Type
    WIN-CON-SINGLEPANE WITH EXTERIOR BLIND,  !- Construction Name of 
the Surface
    ON DUVAR,                !- Base Surface Name
    ,                        !- OutsideFaceEnvironment Object
    0.5000000,               !- View Factor to Ground
    INCIDENT SOLAR ON BLIND, !- Name of shading control
    ,                        !- WindowFrameAndDivider Name
    1.0,                     !- Multiplier
    4,                       !- Number of Surface Vertex Groups -- 
Number of (X,Y,Z) groups in this surface
    0.548000,                !- Vertex 1 X-coordinate {m}
    0,                       !- Vertex 1 Y-coordinate {m}
    2.5000,                  !- Vertex 1 Z-coordinate {m}
    0.548000,                !- Vertex 2 X-coordinate {m}
    0,                       !- Vertex 2 Y-coordinate {m}
    0.5000,                  !- Vertex 2 Z-coordinate {m}
    5.548000,                !- Vertex 3 X-coordinate {m}
    0,                       !- Vertex 3 Y-coordinate {m}
    0.5000,                  !- Vertex 3 Z-coordinate {m}
    5.548000,                !- Vertex 4 X-coordinate {m}
    0,                       !- Vertex 4 Y-coordinate {m}
    2.5000;                  !- Vertex 4 Z-coordinate {m}


!-   ===========  ALL OBJECTS IN CLASS: WINDOWSHADINGCONTROL 
===========

WindowShadingControl,
    INCIDENT SOLAR ON BLIND, !- User Supplied Shading Control Name
    ExteriorBlind,           !- Shading Type
    WIN-CON-SINGLEPANE WITH EXTERIOR BLIND,  !- Name of construction 
with shading
    AlwaysOn,                !- Shading Control Type
    ShadeTransSch,           !- Schedule Name
    20,                      !- SetPoint {W/m2, W or deg C}
    Yes,                     !- Shading Control Is Scheduled
    NO,                      !- Glare Control Is Active
    BLIND WITH LOW REFLECTIVITY SLATS,  !- Material Name of Shading 
Device
    ScheduledSlatAngle,      !- Type of Slat Angle Control for Blinds
    90;                      !- Slat Angle Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: UCSD CROSS VENTILATION MODEL 
CONTROLS ===========

UCSD CROSS VENTILATION MODEL CONTROLS,
    ofis-zone1,              !- Zone Name
    WindowVentSched,         !- Gain Distribution Schedule
    JET;                     !- Airflow region used for thermal 
comfort evaluation


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPE ===========

ScheduleType,
    Control Type,            !- ScheduleType Name
    0:4,                     !- range
    DISCRETE;                !- Numeric Type

ScheduleType,
    On/Off,                  !- ScheduleType Name
    0:1,                     !- range
    DISCRETE;                !- Numeric Type

ScheduleType,
    FlowRate,                !- ScheduleType Name
    0.0:10,                  !- range
    CONTINUOUS;              !- Numeric Type

ScheduleType,
    Any Number;              !- ScheduleType Name

ScheduleType,
    Fraction,                !- ScheduleType Name
    0.0 : 1.0,               !- range
    CONTINUOUS;              !- Numeric Type

ScheduleType,
    Temperature,             !- ScheduleType Name
    -60:200,                 !- range
    CONTINUOUS;              !- Numeric Type


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========

SCHEDULE:COMPACT,
    ShadeTransSch,           !- Name
    Fraction,                !- ScheduleType
    Through: 12/31,          !- Complex Field #1
    For: AllDays,            !- Complex Field #2
    Until: 24:00,            !- Complex Field #3
    0.0;                     !- Complex Field #4

SCHEDULE:COMPACT,
    WindowVentSched,         !- Name
    Any Number,              !- ScheduleType
    Through: 3/31,           !- Complex Field #1
    For: AllDays,            !- Complex Field #2
    Until: 24:00,            !- Complex Field #3
    25.55,                   !- Complex Field #4
    Through: 9/30,           !- Complex Field #5
    For: AllDays,            !- Complex Field #6
    Until: 24:00,            !- Complex Field #7
    21.11,                   !- Complex Field #8
    Through: 12/31,          !- Complex Field #9
    For: AllDays,            !- Complex Field #10
    Until: 24:00,            !- Complex Field #11
    25.55;                   !- Complex Field #12


!-   ===========  ALL OBJECTS IN CLASS: NODE LIST ===========

NODE LIST,
    Zone1Inlets,             !- Node List Name
    NODE_1;                  !- Node_ID_1


!-   ===========  ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP 
CONFIGURATION ===========

CONTROLLED ZONE EQUIP CONFIGURATION,
    ofis-zone1,              !- Zone Name
    Zone1Equipment,          !- List Name: Zone Equipment
    Zone1Inlets,             !- Node List or Node Name: Zone Air 
Inlet Node(s)
    ,                        !- Node List or Node Name: Zone Air 
Exhaust Node(s)
    NODE_4,                  !- Zone Air Node Name
    NODE_5;                  !- Zone Return Air Node Name


!-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST 
===========

ZONE EQUIPMENT LIST,
    Zone1Equipment,          !- Name
    PURCHASED AIR,           !- KEY--Zone Equipment Type 1
    Zone1Air,                !- Type Name 1
    1,                       !- Cooling Priority 1
    1;                       !- Heating Priority 1


!-   ===========  ALL OBJECTS IN CLASS: PURCHASED AIR ===========

PURCHASED AIR,
    Zone1Air,                !- Purchased Air Name
    NODE_1,                  !- Zone Supply Air Node Name
    50,                      !- Heating Supply Air Temp {C}
    13,                      !- Cooling Supply Air Temp {C}
    0.015,                   !- Heating Supply Air Humidity Ratio 
{kg-H2O/kg-air}
    0.010,                   !- Cooling Supply Air Humidity Ratio 
{kg-H2O/kg-air}
    NO LIMIT,                !- heating limit
    autosize,                !- Maximum heating air flow rate {m3/s}
    NO LIMIT,                !- cooling limit
    autosize,                !- Maximum cooling air flow rate {m3/s}
    NO OUTSIDE AIR,          !- outside air
    autosize;                !- Outside air flow rate {m3/s}


!-   ===========  ALL OBJECTS IN CLASS: ZONE CONTROL:THERMOSTATIC 
===========

ZONE CONTROL:THERMOSTATIC,
    Zone 1 Thermostat,       !- Thermostat Name
    RESISTIVE ZONE,          !- Zone Name
    Zone Control Type Sched, !- Control Type SCHEDULE Name
    SINGLE HEATING SETPOINT, !- Control Type #1
    Heating Setpoint with SB,!- Control Type Name #1
    SINGLE COOLING SETPOINT, !- Control Type #2
    Cooling Setpoint with SB;!- Control Type Name #2


!-   ===========  ALL OBJECTS IN CLASS: SINGLE HEATING SETPOINT 
===========

SINGLE HEATING SETPOINT,
    Heating Setpoint with SB,!- Name
    Heating Setpoints;       !- Setpoint Temperature SCHEDULE Name


!-   ===========  ALL OBJECTS IN CLASS: SINGLE COOLING SETPOINT 
===========

SINGLE COOLING SETPOINT,
    Cooling Setpoint with SB,!- Name
    Cooling Setpoints;       !- Setpoint Temperature SCHEDULE Name


!-   ===========  ALL OBJECTS IN CLASS: REPORT VARIABLE ===========

Report Variable,
    *,                       !- Key_Value
    Wind Speed,              !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Wind Direction,          !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone Mean Air Temperature,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    AirflowNetwork Zone Infiltration Volume,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Outdoor Dry Bulb,        !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone Mean Air Temperature,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone Mean Radiant Temperature,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    Zn001:Wall001:Win001,    !- Key_Value
    Surface Ext Solar Incident,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Fraction of Time Shading Device Is On,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Blind Slat Angle, !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Transmitted Solar,!- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Solar Absorbed:All Glass Layers,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Heat Gain,        !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Heat Loss,        !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window Solar Absorbed:Shading Device,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window System Solar Transmittance,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window System Solar Reflectance,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Window System Solar Absorptance,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone/Sys Sensible Cooling Rate,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone/Sys Sensible Heating Rate,  !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone/Sys Air Temperature,!- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Zone Air Humidity Ratio, !- Variable_Name
    timestep;                !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    FangerPMV,               !- Variable_Name
    timestep;                !- Reporting_Frequency


!-   ===========  ALL OBJECTS IN CLASS: REPORT METERFILEONLY 
===========

Report MeterFileOnly,
    Electricity:Facility,    !- Meter_Name
    monthly;                 !- Reporting_Frequency

Report MeterFileOnly,
    Electricity:Building,    !- Meter_Name
    monthly;                 !- Reporting_Frequency

Report MeterFileOnly,
    InteriorLights:Electricity,  !- Meter_Name
    monthly;                 !- Reporting_Frequency

Report MeterFileOnly,
    Electricity:Facility,    !- Meter_Name
    runperiod;               !- Reporting_Frequency

Report MeterFileOnly,
    Electricity:Building,    !- Meter_Name
    runperiod;               !- Reporting_Frequency

Report MeterFileOnly,
    InteriorLights:Electricity,  !- Meter_Name
    runperiod;               !- Reporting_Frequency


!-   ===========  ALL OBJECTS IN CLASS: REPORT ===========

Report,
    Variable Dictionary;     !- Type_of_Report

Report,
    surfaces,                !- Type_of_Report
    dxf;                     !- Name_of_Report

Report,
    construction;            !- Type_of_Report


!-   ===========  ALL OBJECTS IN CLASS: REPORT:TABLE:MONTHLY 
===========

Report:Table:Monthly,
    Zone Cooling Summary,    !- Name
    ,                        !- DigitsAfterDecimal
    Zone/Sys Sensible Cooling Energy,  !- VariableOrMeterName01
    SumOrAverage,            !- AggregationType01
    Zone/Sys Sensible Cooling Rate,  !- VariableOrMeterName02
    Maximum,                 !- AggregationType02
    Outdoor Dry Bulb,        !- VariableOrMeterName03
    ValueWhenMaxMin,         !- AggregationType03
    Outdoor Wet Bulb,        !- VariableOrMeterName04
    ValueWhenMaxMin,         !- AggregationType04
    Zone Total Internal Latent Gain,  !- VariableOrMeterName05
    SumOrAverage,            !- AggregationType05
    Zone Total Internal Latent Gain,  !- VariableOrMeterName06
    Maximum,                 !- AggregationType06
    Outdoor Dry Bulb,        !- VariableOrMeterName07
    ValueWhenMaxMin,         !- AggregationType07
    Outdoor Wet Bulb,        !- VariableOrMeterName08
    ValueWhenMaxMin;         !- AggregationType08

Report:Table:Monthly,
    Space Gains,             !- Name
    ,                        !- DigitsAfterDecimal
    Zone People Total Heat Gain,  !- VariableOrMeterName01
    SumOrAverage,            !- AggregationType01
    Zone Lights Total Heat Gain,  !- VariableOrMeterName02
    SumOrAverage,            !- AggregationType02
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName03
    SumOrAverage,            !- AggregationType03
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName04
    SumOrAverage,            !- AggregationType04
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName05
    SumOrAverage,            !- AggregationType05
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName06
    SumOrAverage,            !- AggregationType06
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName07
    SumOrAverage,            !- AggregationType07
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName08
    SumOrAverage,            !- AggregationType08
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName09
    SumOrAverage;            !- AggregationType09

Report:Table:Monthly,
    Peak Space Gains,        !- Name
    ,                        !- DigitsAfterDecimal
    Zone People Total Heat Gain,  !- VariableOrMeterName01
    Maximum,                 !- AggregationType01
    Zone Lights Total Heat Gain,  !- VariableOrMeterName02
    Maximum,                 !- AggregationType02
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName03
    Maximum,                 !- AggregationType03
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName04
    Maximum,                 !- AggregationType04
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName05
    Maximum,                 !- AggregationType05
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName06
    Maximum,                 !- AggregationType06
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName07
    Maximum,                 !- AggregationType07
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName08
    Maximum,                 !- AggregationType08
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName09
    Maximum;                 !- AggregationType09

Report:Table:Monthly,
    Space Gain Components at Cooling Peak,  !- Name
    ,                        !- DigitsAfterDecimal
    Zone/Sys Sensible Cooling Rate,  !- VariableOrMeterName01
    Maximum,                 !- AggregationType01
    Zone People Total Heat Gain,  !- VariableOrMeterName02
    ValueWhenMaxMin,         !- AggregationType02
    Zone Lights Total Heat Gain,  !- VariableOrMeterName03
    ValueWhenMaxMin,         !- AggregationType03
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName04
    ValueWhenMaxMin,         !- AggregationType04
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName05
    ValueWhenMaxMin,         !- AggregationType05
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName06
    ValueWhenMaxMin,         !- AggregationType06
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName07
    ValueWhenMaxMin,         !- AggregationType07
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName08
    ValueWhenMaxMin,         !- AggregationType08
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName09
    ValueWhenMaxMin,         !- AggregationType09
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName10
    ValueWhenMaxMin;         !- AggregationType10

Report:Table:Monthly,
    Setpoints Not Met With Temperatures,  !- Name
    2,                       !- DigitsAfterDecimal
    Time Heating Setpoint Not Met,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone Mean Air Temperature,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown,  !- AggregationType02
    Time Heating Setpoint Not Met While Occupied,  !- 
VariableOrMeterName03
    HoursNonZero,            !- AggregationType03
    Zone Mean Air Temperature,  !- VariableOrMeterName04
    SumOrAverageDuringHoursShown,  !- AggregationType04
    Time Cooling Setpoint Not Met,  !- VariableOrMeterName05
    HoursNonZero,            !- AggregationType05
    Zone Mean Air Temperature,  !- VariableOrMeterName06
    SumOrAverageDuringHoursShown,  !- AggregationType06
    Time Cooling Setpoint Not Met While Occupied,  !- 
VariableOrMeterName07
    HoursNonZero,            !- AggregationType07
    Zone Mean Air Temperature,  !- VariableOrMeterName08
    SumOrAverageDuringHoursShown;  !- AggregationType08

Report:Table:Monthly,
    Comfort Report - Simple 55,  !- Name
    2,                       !- DigitsAfterDecimal
    Time Not Comfortable Summer Clothes,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone Mean Air Temperature,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown,  !- AggregationType02
    Time Not Comfortable Winter Clothes,  !- VariableOrMeterName03
    HoursNonZero,            !- AggregationType03
    Zone Mean Air Temperature,  !- VariableOrMeterName04
    SumOrAverageDuringHoursShown,  !- AggregationType04
    Time Not Comfortable Summer Or Winter Clothes,  !- 
VariableOrMeterName05
    HoursNonZero,            !- AggregationType05
    Zone Mean Air Temperature,  !- VariableOrMeterName06
    SumOrAverageDuringHoursShown;  !- AggregationType06

Report:Table:Monthly,
    Zone Temperature Oscillation Report,  !- Name
    ,                        !- DigitsAfterDecimal
    Time Zone Temperature Oscillating,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone People Number Of Occupants,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown;  !- AggregationType02

Report:Table:Monthly,
    Zone Cooling Summary,    !- Name
    ,                        !- DigitsAfterDecimal
    Zone/Sys Sensible Cooling Energy,  !- VariableOrMeterName01
    SumOrAverage,            !- AggregationType01
    Zone/Sys Sensible Cooling Rate,  !- VariableOrMeterName02
    Maximum,                 !- AggregationType02
    Outdoor Dry Bulb,        !- VariableOrMeterName03
    ValueWhenMaxMin,         !- AggregationType03
    Outdoor Wet Bulb,        !- VariableOrMeterName04
    ValueWhenMaxMin,         !- AggregationType04
    Zone Total Internal Latent Gain,  !- VariableOrMeterName05
    SumOrAverage,            !- AggregationType05
    Zone Total Internal Latent Gain,  !- VariableOrMeterName06
    Maximum,                 !- AggregationType06
    Outdoor Dry Bulb,        !- VariableOrMeterName07
    ValueWhenMaxMin,         !- AggregationType07
    Outdoor Wet Bulb,        !- VariableOrMeterName08
    ValueWhenMaxMin;         !- AggregationType08

Report:Table:Monthly,
    Space Gains,             !- Name
    ,                        !- DigitsAfterDecimal
    Zone People Total Heat Gain,  !- VariableOrMeterName01
    SumOrAverage,            !- AggregationType01
    Zone Lights Total Heat Gain,  !- VariableOrMeterName02
    SumOrAverage,            !- AggregationType02
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName03
    SumOrAverage,            !- AggregationType03
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName04
    SumOrAverage,            !- AggregationType04
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName05
    SumOrAverage,            !- AggregationType05
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName06
    SumOrAverage,            !- AggregationType06
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName07
    SumOrAverage,            !- AggregationType07
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName08
    SumOrAverage,            !- AggregationType08
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName09
    SumOrAverage;            !- AggregationType09

Report:Table:Monthly,
    Peak Space Gains,        !- Name
    ,                        !- DigitsAfterDecimal
    Zone People Total Heat Gain,  !- VariableOrMeterName01
    Maximum,                 !- AggregationType01
    Zone Lights Total Heat Gain,  !- VariableOrMeterName02
    Maximum,                 !- AggregationType02
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName03
    Maximum,                 !- AggregationType03
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName04
    Maximum,                 !- AggregationType04
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName05
    Maximum,                 !- AggregationType05
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName06
    Maximum,                 !- AggregationType06
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName07
    Maximum,                 !- AggregationType07
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName08
    Maximum,                 !- AggregationType08
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName09
    Maximum;                 !- AggregationType09

Report:Table:Monthly,
    Space Gain Components at Cooling Peak,  !- Name
    ,                        !- DigitsAfterDecimal
    Zone/Sys Sensible Cooling Rate,  !- VariableOrMeterName01
    Maximum,                 !- AggregationType01
    Zone People Total Heat Gain,  !- VariableOrMeterName02
    ValueWhenMaxMin,         !- AggregationType02
    Zone Lights Total Heat Gain,  !- VariableOrMeterName03
    ValueWhenMaxMin,         !- AggregationType03
    Zone Electric Equipment Total Heat Gain,  !- 
VariableOrMeterName04
    ValueWhenMaxMin,         !- AggregationType04
    Zone Gas Equipment Total Heat Gain,  !- VariableOrMeterName05
    ValueWhenMaxMin,         !- AggregationType05
    Zone Hot Water Equipment Total Heat Gain,  !- 
VariableOrMeterName06
    ValueWhenMaxMin,         !- AggregationType06
    Zone Steam Equipment Total Heat Gain,  !- VariableOrMeterName07
    ValueWhenMaxMin,         !- AggregationType07
    Zone Other Equipment Total Heat Gain,  !- VariableOrMeterName08
    ValueWhenMaxMin,         !- AggregationType08
    Zone Infiltration Sensible Heat Gain,  !- VariableOrMeterName09
    ValueWhenMaxMin,         !- AggregationType09
    Zone Infiltration Sensible Heat Loss,  !- VariableOrMeterName10
    ValueWhenMaxMin;         !- AggregationType10

Report:Table:Monthly,
    Setpoints Not Met With Temperatures,  !- Name
    2,                       !- DigitsAfterDecimal
    Time Heating Setpoint Not Met,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone Mean Air Temperature,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown,  !- AggregationType02
    Time Heating Setpoint Not Met While Occupied,  !- 
VariableOrMeterName03
    HoursNonZero,            !- AggregationType03
    Zone Mean Air Temperature,  !- VariableOrMeterName04
    SumOrAverageDuringHoursShown,  !- AggregationType04
    Time Cooling Setpoint Not Met,  !- VariableOrMeterName05
    HoursNonZero,            !- AggregationType05
    Zone Mean Air Temperature,  !- VariableOrMeterName06
    SumOrAverageDuringHoursShown,  !- AggregationType06
    Time Cooling Setpoint Not Met While Occupied,  !- 
VariableOrMeterName07
    HoursNonZero,            !- AggregationType07
    Zone Mean Air Temperature,  !- VariableOrMeterName08
    SumOrAverageDuringHoursShown;  !- AggregationType08

Report:Table:Monthly,
    Comfort Report - Simple 55,  !- Name
    2,                       !- DigitsAfterDecimal
    Time Not Comfortable Summer Clothes,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone Mean Air Temperature,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown,  !- AggregationType02
    Time Not Comfortable Winter Clothes,  !- VariableOrMeterName03
    HoursNonZero,            !- AggregationType03
    Zone Mean Air Temperature,  !- VariableOrMeterName04
    SumOrAverageDuringHoursShown,  !- AggregationType04
    Time Not Comfortable Summer Or Winter Clothes,  !- 
VariableOrMeterName05
    HoursNonZero,            !- AggregationType05
    Zone Mean Air Temperature,  !- VariableOrMeterName06
    SumOrAverageDuringHoursShown;  !- AggregationType06

Report:Table:Monthly,
    Zone Temperature Oscillation Report,  !- Name
    ,                        !- DigitsAfterDecimal
    Time Zone Temperature Oscillating,  !- VariableOrMeterName01
    HoursNonZero,            !- AggregationType01
    Zone People Number Of Occupants,  !- VariableOrMeterName02
    SumOrAverageDuringHoursShown;  !- AggregationType02





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/